Sandeep89

Gas Engineer
Messages
60
Hi Guys,

Needed bit of help on a Vaillant Ecotec 832 which has a pressure issue. The boiler pressure is rising when the CH was running. I have checked the expansion vessle static and charge is showing 1bar on my pump, which I believe means the vessle is good or best to still recharge again? Checked the shrader valve not leaking and no water coming out when pin pushed in.

The boiler has internal filling loop and I removed the filling hose. The filling loop on the flow side is dripping a little. Could this be the cause behind pressure rising as water is letting by into the CH side.

The customer said pressure went to 3.4 bar and display was flashing. I have checked the PRV and it is not letting out water.

Any help would be great. Thanks
 
Did you check the flexi isn’t blocked ?
 
If the filling loop is passing then yes it will cause a rise.
A plate heat ex with a leak from secondary to primary will do same.
Other things that cause a rise could be a blocked pipe leading to the exp vess or an undersized vessel?

Need to know a bit more really.
How old is the boiler?
Is this a new fault?
Does the pressure rise when the boiler is not running? or only when heating is running
 
If the filling loop is passing then yes it will cause a rise.
A plate heat ex with a leak from secondary to primary will do same.
Other things that cause a rise could be a blocked pipe leading to the exp vess or an undersized vessel?

Need to know a bit more really.
How old is the boiler?
Is this a new fault?
Does the pressure rise when the boiler is not running? or only when heating is running
The boiler is 1 year old. Yes the fault is new only started 2 days ago. Pressure rises only heating is running not when the boiler is off. However when the boiler cools down the pressure stays around 1.8 bar and doesn't come down to 1.5bar to which the boiler is pressurised.
 
How strange
Just to confirm you checked the expansion with the boiler drained and the drain off still open?
Yeah so isolated return and flow, drained down boiler and left drain off open. The static reading was 1 bar.

Yeah I know, I am going to leave the filling loop hose off and then run the heating and monitor to at least eliminate the filling loop.

Talking about vessles total random question but had a boiler few months trying to recharge the vessle however no water was coming out from the drain off when pumping the vessle. Any ideas on that.
 

Reply to Vaillant Ecotec 832 pressure rise with CH on in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
1
Views
78
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new brackets, dismantle that existing one and start again or I could try and re attach via those screws, removing the broken ones from the plate and wall...
Replies
1
Views
175
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
301
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
382
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
173
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock