Hi all, I’ve got an issue with no hot water from Center 300L unvented Cylinder on S Plan plus system. All Electrical controls working fine. Only way to get hot water to the taps is by using immersion heater. Any ideas what could be up? Thanks in advance.
 
Is the port valve working / opening ?
 
And you could open the body via the spindle easily ?
 
Should move easily 12- 2
 
Need to check when you turn hw on via your controls the brown from the hw two port has 240v with a multi meter
 
Need to check when you turn hw on via your controls the brown from the hw two port has 240v with a multi meter
I’m a Spark, I’ve checked that it all switches right. I confirmed that if the cylinder stat is calling for heat on the cylinder, the zone valve fires and gas on boiler ignites. All working fine. Just no hot water at taps unless like I say, I put the separate immersion heater switch on for a few hours.
 
Do you have hot water going through the port valve ?
 
But does the pipe get red hot ?
 
And it heats for a good hour eg the flow pipe stays hot ?
 
And it heats for a good hour eg the flow pipe stays hot ?
Yes it seems to, the boiler gets right up to about 85 degrees and then the gas light goes off, I’m guessing that’s the boiler doing it’s job, even if the cylinder is still calling for heat. Only literally a bowl full of hot water, then runs cold again
 
How long do you have hot water on its own for ?

And heating is fine ?
 
Yes, the pipe that goes to the primary into the cylinder is jumping hot.

Take the case when the cylinder is cold, and you haven't had the immersion on.
The pipe that feeds the primary coil is "jumping hot"
At that instant, is the return out of the cylinder coil also pretty hot?

It should be a bit cooler, but if it's the same temperature as that area of the tank, I was wondering if there's a circulation problem in the cylinder coil circuit - poor flow leading to a lack of energy transfer?
 
Take the case when the cylinder is cold, and you haven't had the immersion on.
The pipe that feeds the primary coil is "jumping hot"
At that instant, is the return out of the cylinder coil also pretty hot?

It should be a bit cooler, but if it's the same temperature as that area of the tank, I was wondering if there's a circulation problem in the cylinder coil circuit - poor flow leading to a lack of energy transfer?
Had a plumber out today, he said that maybe there’s a build up of limescale or whatever in the tank. 13 years installed. Is this even possible? He said new tank needed
 
Had a plumber out today, he said that maybe there’s a build up of limescale or whatever in the tank. 13 years installed. Is this even possible? He said new tank needed
Not really my area of expertise. But I will say I had a house in a very lime scale rich area of the country, the old fortic tank immersion heater went, and when I removed it I found the bottom of the tank was inches deep in limescale 'platelets'.
I dug it all out, fitted a new immersion, and all worked fine.

I'm assuming your plumber is inferring there's a build-up of limescale on the coil, rather than just in the bottom of the tank, because surely the latter could be rectified without changing the cylinder!
I'm not clear if your mystery lack of H/W is something that suddenly happened, or if it's been inherited. If it's happened suddenly, I don't think the limescale theory "holds water"🤪.

I'd be wary of changing things before understanding what is causing the problem.
 
Not really my area of expertise. But I will say I had a house in a very lime scale rich area of the country, the old fortic tank immersion heater went, and when I removed it I found the bottom of the tank was inches deep in limescale 'platelets'.
I dug it all out, fitted a new immersion, and all worked fine.

I'm assuming your plumber is inferring there's a build-up of limescale on the coil, rather than just in the bottom of the tank, because surely the latter could be rectified without changing the cylinder!
I'm not clear if your mystery lack of H/W is something that suddenly happened, or if it's been inherited. If it's happened suddenly, I don't think the limescale theory "holds water"🤪.

I'd be wary of changing things before understanding what is causing the problem.
I would agree with you. This system was nee 13 year ago, can’t think we live in a high lime scale build up area, I’m trying to speak to Baxi re the cylinder, was on hold too long today. I’ve messaged them, hopefully they call back, I would also want to find out the issue rather than just replace
 

Reply to Unvented Center cylinder no hot water in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Afternoon. I have an issue with no water flow from any of the hot taps in the house, I can't seem to find a solution to the issue. System is a megaflo unvented indirect cylinder (125i) boiler is a Worcester greenstar. I have good pressure on the cold feed and all the usual stuff works, taps...
Replies
11
Views
287
Hi, I'm in my new build 2 years and the shower pump has died. I have an air to water unit downstairs is in the utility which I've been told is unvented and pressurised. The cold water feed into this cylinder is from the attic tank, not the mains as I turned off the mains stopcock to see if hot...
Replies
6
Views
160
I need to change my shower mixer and I have a unvented hot water cylinder. Is it sufficient to turn off the mains? Do I need to drain the cylinder? Thanks
Replies
0
Views
341
Hi There was no shut off valve on the tank feed to the hot water cylinder, and I needed to move a couple of hot water pipes, so I shut off the mains water, turned boiler off (Remeha avanta) and opened the hot kitchen tap to drain the cylinder. After doing the work etc, Everything up and...
Replies
4
Views
213
I live in an apartment block where generally hot water is supplied from the communal hot water cylinder and cold water to bathrooms is supplied from cold water tanks in the loft. It is a vented system. However, in a basement flat and a ground floor flat cold water supply to bathrooms is...