Hi there 👋🏾

Hoping that someone might be able to take the time to help me understand our central heating system.

We recently moved in to a relatively new, 4-bed semi-detached house (2015), having come from a 2-bed flat. The new house has three floors, with a ground floor WC, first floor bathroom and second floor en-suite.

The flat had a combi boiler only; very straightforward to understand.

Here we have a tank, which is described as an indirect unvented water heater and "conventional" boiler.

I've got three issues - possibly connected:

1) in redecorating we had one of the radiators removed and drained. Whilst we were able to bleed it to get it filled again, this seems to have drained one of the second floor rads - I've tried bleeding them and one doesn't hiss with air or return water...any ideas?

2) the pressure gauge near the hot water tank was at around 1.5 bar after the radiator was replaced, but now seems to have dropped - I would assume I need to open the two valves in the attached picture near this small tank (no idea what this does)?

3) the pipes near the tank itself male hissing sounds intermittently - not sure if I should be worried?

Thanks
 

Attachments

  • 20210829_185402.jpg
    20210829_185402.jpg
    152 KB · Views: 14
  • 20210829_185343.jpg
    20210829_185343.jpg
    191.4 KB · Views: 14
  • 20210829_185331.jpg
    20210829_185331.jpg
    94.8 KB · Views: 15
  • 20210829_185324.jpg
    20210829_185324.jpg
    110.8 KB · Views: 13
you need to top up using those two valves open them allow to approx 1.5 bar bleed you r rads and repeat until all full pressure in system when cold should be 1 to 1.5 bar 1.5 is where the red pointer is
 
you need to top up using those two valves open them allow to approx 1.5 bar bleed you r rads and repeat until all full pressure in system when cold should be 1 to 1.5 bar 1.5 is where the red pointer is
Thanks for the swift response - I'll give this a go.

In theory, should this deal with the second floor rads too? Being that they are above the hot water tank?
 
When you bled the lower rad, the water to fill it came from the second floor rads- you just moved around the water that was in the system.

When you use the black valves on the filling loop the water comes from the mains so you are adding water to the system, when you bleed the air out all will be fine - it may take a couple of goes .
 
Thanks @Ben-gee and @Undertrained - bit delayed in my response, but I got it sorted (though, I reckon the system needs flushing now as some rads are cold at the bottom and hot at the top...)
When you bled the lower rad, the water to fill it came from the second floor rads- you just moved around the water that was in the system.

When you use the black valves on the filling loop the water comes from the mains so you are adding water to the system, when you bleed the air out all will be fine - it may take a couple of goes .
 

Reply to Understanding the system and rad issues in the USA area at PlumbersForums.net

Similar plumbing topics

Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
207
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
256
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
176
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock