I have a OMNIE designed wet underfloor heating system on three floors. Ground and 2nd floors work well with those two floors having a single manifold and recirculating pump for the various zones.
On the 1st floor the rooms are split over two manifolds each with its own recirculating pump. However, the dressing room and en-suite shower room which is two zones controlled from one wall thermostat/control is split between two manifolds.
When I call for heat one actuator on one manifold switches on and the recirculating pump starts. However, the 2nd zone to the other actuator and manifold does not seem to activate in that the recirculating pump does not activate and the control box for that manifold does not light up indicating it is activated although the actuator nipple rises. Pipes remain cool.

I have attached photos of manifolds and floor design. My question is why split common zones over two manifolds and two recirculating pumps? This does not seem a good design or cost effective.

Has anyone got a view on this please.
 

Attachments

  • B3625C63-389F-4EF5-9634-103477BFF115.jpeg
    B3625C63-389F-4EF5-9634-103477BFF115.jpeg
    276.5 KB · Views: 6
  • 7682DEB6-4968-4DC5-9128-0E14554DCD15.jpeg
    7682DEB6-4968-4DC5-9128-0E14554DCD15.jpeg
    74.1 KB · Views: 7
  • FD7F11BA-E537-4F6D-9FF3-9D27C8352C6D.png
    FD7F11BA-E537-4F6D-9FF3-9D27C8352C6D.png
    1.6 MB · Views: 6
  • F41297BC-8962-4948-A414-894A1AE6840B.png
    F41297BC-8962-4948-A414-894A1AE6840B.png
    1.5 MB · Views: 5
Are they on there own stats ?
 
so the dressing room and ensuite has one room thermostat which is in the dressing room. I’ve tried turning this right up to actuate both zones but only the dressing room heats up. They are right next to one another.
 
Well yes then wrong need to speak to the installers to see if they have missed a stat off if not they need to be linked etc
 
OMNIE have confirmed my installer has wired this up incorrectly as I had surmised.

Wired and plumbed up as really the same zones should be on the same manifold
 

Reply to Underfloor wet system design query in the Water Underfloor Heating Advice area at PlumbersForums.net

Similar plumbing topics

Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
207
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new brackets, dismantle that existing one and start again or I could try and re attach via those screws, removing the broken ones from the plate and wall...
Replies
0
Views
116
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
5
Views
134
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock