helpsy

Plumbers Arms member
Plumber
Gas Engineer
Messages
1,754
Any info on how above works etc appreciated....not had any dealings with it yet. My Dad up in Scotland has wet underfloor heating and is having some problems with it. Thanks
 
basicly the water is mixed at the manifold to deliver cooled water through the underflooor each circuit of the manifolds is balanced with valves at the manifolds to even out flow realy need to know what the problems are to offer more help
 
Cheers Steve....he said some ares are warm others not.....so I guess it's a balancing issue potentially then ?!
 
You shouldn't need to balance it as flow heads on manifolds should be set to within 5% of design?

Have u tried unscrewing the actuator heads to check that it's not actuator / elec fault? Has the system been drained or modified? If it had been drained possible air ? Also if drained don't forget biocide. Af10 is simplest one for system.
 
Status
Not open for further replies.

Reply to Underfloor heating in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I'm attending a wet underfloor heating system, it's an old one ..No flow meters, just adjustable valves on the returns with conventional actuators. Problem is , one loop (far right in photo) isn't heating the floor (timber suspended) . I've bled the loop via a hosepipe, shut off all the other...
Replies
3
Views
501
We have UFH throughout downstairs. I have had one coil replaced. I have had the thermostats checked that they are linking to the correct actuators, which they are. the cupboard where the UFH system is gets hot when I turn up the thermostats in one or all zones. The boiler is coming on but the...
Replies
8
Views
578
Hi folks, hoping someone can help with a problem that's been perplexing me since just before Christmas..... I have a wet underfloor heating system installed in 2003 and manufactured by Underfloor Direct in NI - Now out of business. It's one of their triple tube systems and hasn't given me much...
Replies
19
Views
1K
We have a Daikin Air Source heat pump feeding our hot water and under-floor 8 port manifold heating system. The Daikin has just had its annual service and the engineer commented that the water looked discoloured and that the inhibitor needed replacing?? Is this an easy procedure? I'm pretty...
Replies
0
Views
326
Hi All, Looking for a bit of advice on the best way to pipe this. - 24kW Worcester regular boiler in kitchen, approx. 9 years old - unvented tank, zone vavles, pump, expansion is on first floor in airing cupboard - Currently piped as S-plan. - Hive controls. - Would like to fit 6-zone...
Replies
16
Views
971