J

JSlippy

We’ve had a UFH system installed as part of our home renovation which is run alongside our existing radiators. Some of it is in rooms with LVT flooring which means we’ve got to be careful with water temperature (floor temp limits are set, but can easily overshoot if water is too hot).

Our problem is that sometimes the mixing valve shuts the flow down completely even when the UFH pipes are cold. Today our lounge wasn’t warming up so I checked the system. The pump was running but all flow meters were at zero. The temperature going into the manifold was about 30 degrees, but the return temp from the manifold was about 40.

Presumably the mixing valve closed completely when the return temperature reached 40 degrees. But because the valve is closed, it can’t detect when the water in the UFH pipes falls (for example if a different room calls for heat).

I turned the mixing valve setting from 4 to 6, which instantly sent flow through the system and the return temperature dropped like a stone! I was able to drop the valve back to 4 and it worked as normal.

Surely this isn’t the way the system is supposed to work. I understood that the mixing valve was supposed to blend water from the boiler with the manifold return, but keep water flowing through the UFH pipes the whole time. That clearly isn’t happening here, does that indicate a problem with the way the system is set up?

The pump is a Grundfos UPS3, mixing valve is ESB VTG141. We can get the installers out but there's no chance I'll be able to replicate the problem for when they're here! If anybody has any tips on whether this is expected behaviour or what should really be happening, it would be appreciated!
 

Reply to Underfloor heating mixing valve issues in the Water Underfloor Heating Advice area at PlumbersForums.net

Similar plumbing topics

Do people with this type of mixed flow temperature control have any problems with achieving the required manifold flow temperature? The one below I think is similar to the TIO Mixing unit. In the unit below, the hot (boiler) water enters from the bottom left, red arrow, up through the "mixing...
Replies
3
Views
538
A
I have a UFH manifold from Wundatrade with a Grundfos pump. The pump feed has a mixing valve which has a hot inlet from the thermal store, and a cold inlet from the return manifold. In-between the mixing valve cold inlet and the return manifold, is a tee which returns the cold water to the...
Replies
20
Views
3K
I have NuHeat UFH system, and this has no Thermostatic Blending valve on the heating circuit. (Heat Master II cylinder has pick up coil) Nu-Heat System installed - This means I can't run store above 60C due to risk of overheating UFH pipes. I want to add a Thermostatic Mixing valve so have...
Replies
8
Views
852
Hi, I have a combi boiler that supplies hot water to two ufh manifolds. We only have ufh and no radiators. I am trying to find the most efficient way to heat our home. What would your recommendations be on the following ways to set our system up. A) Set the ufh mixer to max so it isn't doing...
Replies
1
Views
1K
Are there fundamental differences in some of these TMVs?. The attached one, below, would seem to be the better type where a shuttle moves to balance the hot&cold flows, as it increases one flow it decreases the other to keep the mixed flow constant, necessary say in showers etc. I have seen...
Replies
1
Views
958
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock