Discuss UFH Pump - Always on? in the Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Messages
18
Reaction score
3
Hi all,

I've had a Polypipe UFH solution fitted and I've got a query about the water-pump. I've asked the plumber but he's passed me onto the spark - who fitted it this way. Kinda think between them I've not got a definitive answer...so here I am asking the plumbing gurus...

In a nutshell - this pump, I'm assuming, is constantly on. The green light is on, and it omits a sound, from the pump and the pipes. Its not pumping hot water because the thermostat isn't calling the boiler but I feel its pumping cold around the system 24/7?

I've got the plumber and a spark coming round tomorrow, so looking to gear myself up with some knowledge

Can anyone offer me any advice please?

Cheers, Mark

IMG_4837.jpg
 
Test4Less - PlumbersForums.net Sponsor
This official sponsor may provide discounts for members

ShaunCorbs

S. Mod
Plumber
Gas Engineer
Messages
23,544
Reaction score
6,431
It’s always pumping which is wrong

Also there’s looks no independent control of the zones so there all on
 
OP
M
Messages
18
Reaction score
3
thanks for that swift reply Shaun; does this photo help with regards to the independent controls.. what should I be expecting?

Cheers, Mark

31CEC888-4A36-4041-B5B7-221D0CEAFA85.jpeg
 

king of pipes

Plumber
Gas Engineer
Messages
3,219
Reaction score
1,283
Your underfloor heating zone should have its own time and temperature controls and switch the pump off when either the stat is satisfied or the zone is not in a timed on mode I would expect to see a 2 port zone valve and a timer of some sort. Regards kop
 
OP
M
Messages
18
Reaction score
3
image.png Got ya, it’s got a Nest Thermostats connected to the boiler and a value. That pump seems to be just plugged in to perm power... should it be switched in some way
 
Last edited:
Messages
306
Reaction score
158
With due respect whoever installed that system does not understand the concept of how a wet underfloor system operates. I would suggest that you get a credible plumber in to correct the faults, set up and balance the system properly.

You really should not be employing tradesmen who you have to tell them the basics about what is wrong / missing with the installation they have left you with
 
Last edited:
OP
M
Messages
18
Reaction score
3
I totally hear you! Unfortunately, as many pre and post me. I have fallen into the trap of being told they are credible professionals and can install my solution. Getting someone else in could sort or exacerbate my issue..
 
Messages
306
Reaction score
158
I can sympathise with your position - but you probably need to recognise that this is probably their first time installation with wet underfloor system
 
Last edited:

king of pipes

Plumber
Gas Engineer
Messages
3,219
Reaction score
1,283
View attachment 39206 Got ya, it’s got a Nest Thermostats connected to the boiler and a value. That pump seems to be just plugged in to perm power... should it be switched in some way
Yes the pump needs to be wired into the correct connector blocks in series with the underfloor controls it very much looks like a wiring issue . Kop
 

Chalked

Plumber
Gas Engineer
Messages
4,954
Reaction score
2,306
Best to disconnect the nest from the ufh. It can’t anticipate the heat and cooling demands.
 

Jones82

Gas Engineer
Messages
174
Reaction score
38
I think the nest has an underfloor heating setting? It certainly has a "radiator" option. I think the trouble here is the pump has a permanent live, likely from a crossed wire with the grey on the 2 port valve... assuming there is one!

Does the pump run even when the boilers off?
 
Messages
306
Reaction score
158
Nest works with both electric and wet underfloor heating systems. The latter must be properly designed and well balanced to deliver a consistent and even heat pattern to give Nest a chance to work effectively.

The normal issue ( problem) is that the Nest Heatlinks for multiple zones are placed too close together and too close to “significant” metallic objects - multiple copper pipes or hot water storage tanks. Heatlinks should be spaced at least 300mm apart, preferably a lot more. To be fair this is an issue ( signal interference) with the Honeywell wireless systems too
 
Last edited:
OP
M
Messages
18
Reaction score
3
Hi Jones, the pump shows the green light always, and makes a very low sound, which is mirrored through the pipes. So I’m assuming it’s doing something... even when the boiler isn’t being called.

I think the nest has an underfloor heating setting? It certainly has a "radiator" option. I think the trouble here is the pump has a permanent live, likely from a crossed wire with the grey on the 2 port valve... assuming there is one!

Does the pump run even when the boilers off?
 
Messages
306
Reaction score
158
Yes, it is. Probably circulating cold water 24 hours / day.

Generally, Wet Under Floor Heating Systems are silent to the human ear - well they are to mine anyway!!
 

Jones82

Gas Engineer
Messages
174
Reaction score
38
The pump live needs connecting into the switched live for the underfloor heating zone, usually the white cable on the 2 port valve that controls the underfloor heating zone.
 

Uheat – Jake

Sponsor
Messages
31
Reaction score
17
As Jones says, just a simple wiring issue. The pump will have a permanent live to it when it only needs a switch live which will become live when your nest thermostat is calling for heat.
 
Plumbase - PlumbersForums.net Sponsor
Power Shower Booster - Official PlumbersForums.net Sponsor
Corgi Direct - Plumbers Forums Sponsor
uHeat Forum Sponsor - PlumbersForums.net
Plumbing Advice - Find Plumbers Jobs
Test4Less PlumbersForums.net Sponsor
Wetroom Store - PlumbersForums.net Sponsor

Latest Plumbing Advice

Top Bottom