P

Pickled eggs

Hello,

We are having wet UFH installed across the ground floor of our house, about 5 zones. We'd like vinyl and timber and hence know we need to limit the floor temp to 27 degrees; question what are the ways to do this?

We've seen the neo control system that can control on air temp and floor probe temp.

We're keener on the hive system, but we'd need a secondary control for the 27 degree cut off. This must be the same as having standard room stats - how is floor temp controlled in that situation?

Many thanks
Joanne
 
I was going to say exactly the same thing as Shaun, Wojtek is the man :)
 
Just fit floor temperature probes into all floors with vinyl. Then set the stat limit to 27.
Forget the hive, they are useless at controlling underfloor heating. There is too much lead and lag with underfloor for a predictive thermostat..
 
  • Like
Reactions: rpm
neo stats all day long you can get a hub to control neo stats from your phone why would you need hive?
 
Just run the flow temperature at 45C.
Without going into calculations and reasoning of calculations, a flow temperature of 45C will give you an average floor temperature of 27C - 28C - give or take.
 
Personally I wouldn't recommend hive thermostats. waste of time and money. not just heatmiser, but quite a few decent quality thermostats allow user to set probe limit whilst using air sensor to control the room temperature.
 
Status
Not open for further replies.

Reply to UFH floor temp control in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
122
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
200
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
5
Views
139
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
5
Views
144
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
256
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock