Hello everyone, I'm a Plumber/ pump man from the Philippines. I need advice regarding pump problem. I dont know if this the right forum, but here it is. Two pumps connected in parallel runs continuously. What puzzled me is that whenever I partially closed main discharge valve or any of the discharge valve of both pump the pressure drops. Now this my first encounter with such a pump. Please refer to attached files. Is it perhaps a variable speed/ discharge pump that reacts to the pressure transmitter installed at the discharge. Pump is servicing a four story building. pressure is 70 psi drops to 50 to 60 whenever I partially close any discharge valve. Looking forward to your advice.
 

Attachments

rpm

Esteemed
Plumber
Grundfos CR10`s 12m head multi-stage booster pumps there. One speed non variable 3kw motors @ 3500rpm and no pressure transmitter on them. Don`t understand why you would want to throttle back the discharge or are you getting cavitation.
 
Grundfos CR10`s 12m head multi-stage booster pumps there. One speed non variable 3kw motors @ 3500rpm and no pressure transmitter on them. Don`t understand why you would want to throttle back the discharge or are you getting cavitation.
I'm just testing if the pump can still deliver more pressure. There is a pressure transmitter installed next to the pressure gauge.
 

Danb

Gas Engineer
Is that the boosted cold
Post automatically merged:

Does it feed a tank onntop of the four storys?
Post automatically merged:

Its trying to maintain a constant pressure.
When you close it do you only lose pressure on one side
 
Last edited:

rpm

Esteemed
Plumber
What is this pressure transmitter, can you post photos of it please?
Post automatically merged:

I'm just testing if the pump can still deliver more pressure. There is a pressure transmitter installed next to the pressure gauge.
Is that the boosted cold
Post automatically merged:

Does it feed a tank onntop of the four storys?
Looks like it is in a workshop at the moment.
 
Last edited:
Is that the boosted cold
Post automatically merged:

Does it feed a tank onntop of the four storys?
Post automatically merged:

Its trying to maintain a constant pressure.
When you close it do you only lose pressure on one side
Yes it is boosted cold
No it does not feed a tank on the top floor it has a pressure tank next to it.
Its connected in parallel so both lose pressure. Yes I think its trying to maintain a constant pressure
Post automatically merged:

What is this pressure transmitter, can you post photos of it please?
Post automatically merged:



Looks like it is in a workshop at the moment.
The transmitter has a wire that runs to the control board. That is why I was thinking that maybe " the control board sends command to the motor based on the transmitter reading" That is why I was thinking the motor is variable speed. I dont see an auto bypass valve either.
Post automatically merged:

there is only one pressure gauge on the discharge side of both pumps that sits next to the pressure transmitter.
Post automatically merged:

The pressure transmitter is connected to the pressure gauge with a tee and has wire that goes to the control board
Post automatically merged:

I think the reason it runs continuously is because its trying to maintain a constant pressure that does not go up to the set cut out pressure.
Post automatically merged:

I am sorry I think I had said something wrong. Please refer to the layout drawing I made as I try to explain. Actually the discharge valve1 is currently 20% or so open so like 80% close. Whenever I try to open it pressure drops. When I close main discharge valve pressure also drops. So yes I think its trying to maintain a constant pressure. But if it does, why does the pressure dont recover. I have watch there for like 2 min and the pressure never recover. How long does a pressure of such a system recovers? Whenever I close main valve or open valve1 pressure drops within a minute.
 

Attachments

Last edited:

rpm

Esteemed
Plumber
It won`t recover pressure, are you getting flow & pressure mixed up. A quick look at Grundfos site say`s outlet should be DN40 which I don`t think you`re showing in the photographs. You won`t get more out than the manufacture states by adjusting inlet/ outlet valves, if anything you will kill it.
 

Danb

Gas Engineer
Looks to me the the pressure transducer notices pressure drop and kicks selected pump in. When its satisfied turns them off.
If there no non returns with the head off water it pass back through pump 1 when you open valve 1.
Also whats the min and max pressure settings set at?
Post automatically merged:

The pressure tank next to it that you mentioned,
Should think this is more likely the cold feed for the pump to make sure it has volume behind it .
Post automatically merged:

Agree with rpm these are on off pump sets.
 
Last edited:

rpm

Esteemed
Plumber
You mentioned increasing the pressure , you can buy a service kit for these if they are down on duty. I've recon these on site lots of times.
 
Looks to me the the pressure transducer notices pressure drop and kicks selected pump in. When its satisfied turns them off.
If there no non returns with the head off water it pass back through pump 1 when you open valve 1.
Also whats the min and max pressure settings set at?
Post automatically merged:

The pressure tank next to it that you mentioned,
Should think this is more likely the cold feed for the pump to make sure it has volume behind it .
Post automatically merged:

Agree with rpm these are on off pump sets.
two pumps run continuously 24/7. But you're right there is no non returns on the head off. I think you're correct with the pressure tank because its just a small one. Not the size to service an entire building. that solves one of my concerns. Excuse my ignorance but what is an "on off pump set"
 

snowhead

Plumber
Excuse my ignorance but what is an "on off pump set"
When the pressure drops below the cut in set point the pump(s) switch ON and run at their maximum speed.
When the pressure in the system reaches the cut off set point, the pump(s) switch OFF.

Modern pump systems are variable speed, so the pump(s) reduce speed to keep the pressure constant.

Have you checked that there is no air trapped in the pumps?
 

oz-plumber

Esteemed
Plumber
Quite a lot of variables with this one and it could be a situation where you start with the basics and go on from there.

1/ non-return valves on outlets of pumps
2/ pressure switches - faulty, not calibrated, not connected.
They are there, but not switching off the pumps - obviously not working as intended.
3/ Pressure vessel - shouldn't have much to do with the operation of the pumps or pressure switches on the pumps. It's only there to stop a lag in water pressure when the pumps are stopped and the pressure switch hasn't activated ( very basic description of what it does )
 

rpm

Esteemed
Plumber
Unless I`m looking at this all wrong I would expect to see two pressure gauges on the discharge pipes or one on the pipe after they merge together if they do this.
Also wondering if a photo of the control board might help.
 
There seems to be two different pumps fitted, one is 12.1 m3/hr, 47.2 M head @ 3550 RPM, the other nameplate shows a 50HZ pump, 2990 RPM, can't see the flow/head so if fitted in the philippines will run at 60 HZ so maybe thats fitted in position 1 and throttled in to prevent o/load trip out (pump affinity laws). If so, it seems a very strange match but whatever the set up, there should most certainly, as pointed out above, be NR valves fitted because not only will you get reverse flow through the pump, you can/will also get reverse rotation of the pump which will result in motor burnout on auto restart or if restarted without manually shutting the discharge valve.
 
Last edited:
There seems to be two different pumps fitted, one is 12.1 m3/hr, 47.2 M head @ 3550 RPM, the other nameplate shows a 50HZ pump, 2990 RPM, can't see the flow/head so if fitted in the philippines will run at 60 HZ so maybe thats fitted in position 1 and throttled in to prevent o/load trip out (pump affinity laws). If so, it seems a very strange match but whatever the set up, there should most certainly, as pointed out above, be NR valves fitted because not only will you get reverse flow through the pump, you can/will also get reverse rotation of the pump which will result in motor burnout on auto restart or if restarted without manually shutting the discharge valve.
Edit: Maybe both 60hz pumps have 50 hz motors fitted and the installation is in the UK.
 
When the pressure drops below the cut in set point the pump(s) switch ON and run at their maximum speed.
When the pressure in the system reaches the cut off set point, the pump(s) switch OFF.

Modern pump systems are variable speed, so the pump(s) reduce speed to keep the pressure constant.

Have you checked that there is no air trapped in the pumps?
Ok so this is not a variable speed pump and I should stop looking from that angle.
I will try to air purge the pumps.
Post automatically merged:

Quite a lot of variables with this one and it could be a situation where you start with the basics and go on from there.

1/ non-return valves on outlets of pumps
2/ pressure switches - faulty, not calibrated, not connected.
They are there, but not switching off the pumps - obviously not working as intended.
3/ Pressure vessel - shouldn't have much to do with the operation of the pumps or pressure switches on the pumps. It's only there to stop a lag in water pressure when the pumps are stopped and the pressure switch hasn't activated ( very basic description of what it does )
You could be correct about all of these. But how does this correlate to the dropping of pressure whenever I make adjustment on valves that is suppose to increase pressure. If pump maintains speed and power closing outlet valve should increase pressure in between valve and pump where the pressure gauge (and transducer) is located, no exception. also opening valve one full (which is currently about 20% open) should increase pressure, but the opposite happens. What other explanation could there be, if there is any. other than the pump is "trying to maintain a constant pressure". You see I don't want to touch anything until I am able to connect all the dots. This is a hotel and I don't want to trouble the guests as that won't be good for the owners.
Post automatically merged:

Unless I`m looking at this all wrong I would expect to see two pressure gauges on the discharge pipes or one on the pipe after they merge together if they do this.
Also wondering if a photo of the control board might help.
I will take photo of the control board and more photo of the system when I go visit again. I am not hurrying with this one. I told the client that I wont touch anything unless I am absolutely sure of what to do and that they can hire someone if they want to.
 
Last edited:

Danb

Gas Engineer
Without seeing the set up is hard to say for certain but It looks like to me that there for constant cold pressure.
As mentioned earlier.
Fit nrvs for a start.
Check min and max pressure settings, mechanical or digital control.
Make sure pump supply tank.is large enough to cope with demand,
As mentioned earlier you may get air in system if the tank runs dry And get pump issues.
 

Reply to Two pumps connected in parallel runs continuously in the Plumbing Forum | Plumbing Advice area at PlumbersForums.net. Plumbing questions, answers, tips and tricks.

Bulk Workwear - Workmans Clothing and Protective Gear
This official sponsor may provide discounts for members
Plumbase - PlumbersForums.net Sponsor
Corgi Direct - Plumbers Forums Sponsor
Power Shower Booster - Official PlumbersForums.net Sponsor
Wetroom Store - PlumbersForums.net Sponsor
uHeat Forum Sponsor - PlumbersForums.net
Test4Less PlumbersForums.net Sponsor
Bulk Workwear - Workwear Sponsor for Plumbers Forums
Plumbing Advice - Find Plumbers Jobs

New Posts Threads Members

Bulk Workwear - Workmans Clothing and Protective Gear
This official sponsor may provide discounts for members
Top