Hello all,
Please help a football deprived wrinkly.
I've recently moved in our new house (20yr old) but all's not well. One radiator keeps filling up with air? It's a alien system (thought would be a condensing combi being a newish house) to me as we've got a boiler and a hot water storage, cylinder with 2 water tanks (1 large 1 small)
What I know usually there's a loop and a pressure valve but I can't find either to fill up the radiator?
Is it possible it self pressurizes ?
I feel wrong to let more air out of the one radiator if there's no water in the system.
Please help because I ain't got much hair left to pull out.
Thank you for any replies in advance
Ps it's make is Main heating condensing boiler.
Paddy
 
It’s an open vented system, the smaller loft tank is used to keep the radiators and pipework full of water so wen you bleed a radiator water will flow into it.
Although if you have to bleed it a lot then you may have an issue, maybe it’s not set up properly and is sucking air in, difficult to say for sure without having a closer look at it.
Thanks Stuart for your time, i really appreciate it. There is a dust cap like fitting on a inlet to the hot water tank which does drip every now & again?
I'll bleed the radiator again and if it fills with air again I'll get the professionals in.
Thanks again Stuart!
Paddy
 
As Stu says, your type of system is self-filling.
Thanks Stigster, I appreciate your time. Seems a weird system to have in a new house, the space it takes up is unreal. The women we bought the house off said it was a emersion heater for the water & boiler did the water? But that was just one of many lies told. Think a combi boiler would be a better idea seems a simpler system? Not sure what the positives having this system yet?
Kind regards
Paddy
 
Sometimes air is drawn in to a heating system on the vacuum side (upstream side) of the circulating pump causing build up in one or more radiators, among other potential causes of course. The simplest thing to try is to see if you can nip up the nut on that side of the pump using a huge adjustable spanner or more sensibly a pair of water pump pliers AKA grips. If you decide to do this you'll need to hold the body of the valve tight with an appropriate tool to stop it moving as you tighten the nut against the pump.

I must warn you though that moving a fitting can occasionally cause a weep but tightening is usually sound. Depending upon your DIY confidence levels, this is something you can try that isn't too difficult. If the pump valve is in good condition it won't cause a flood just trying to tighten it and it is the first thing I would do.

There can be other causes of air ingress but tightening that pump nut is probably the easiest thing to do and I have found it to be the cause of the problem enough times for it to be worth a go. If it doesn't fix it there are other things we can advise you to look at.
 
Sometimes air is drawn in to a heating system on the vacuum side (upstream side) of the circulating pump causing build up in one or more radiators, among other potential causes of course. The simplest thing to try is to see if you can nip up the nut on that side of the pump using a huge adjustable spanner or more sensibly a pair of water pump pliers AKA grips. If you decide to do this you'll need to hold the body of the valve tight with an appropriate tool to stop it moving as you tighten the nut against the pump.

I must warn you though that moving a fitting can occasionally cause a weep but tightening is usually sound. Depending upon your DIY confidence levels, this is something you can try that isn't too difficult. If the pump valve is in good condition it won't cause a flood just trying to tighten it and it is the first thing I would do.

There can be other causes of air ingress but tightening that pump nut is probably the easiest thing to do and I have found it to be the cause of the problem enough times for it to be worth a go. If it doesn't fix it there are other things we can advise you to look at.
Thanks stigster, are these the two large nuts that need to be tightened.
Again thanks for your time.
Kind regards paddy
 

Attachments

  • 20200114_205750.jpg
    20200114_205750.jpg
    81 KB · Views: 8

Reply to Too much air not enough hair in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

When I turn on our CH there's a lot of noise from one specific part of the system - the pipes on the landing, and one radiator. It sounds like air, and the landing radiator needs bleeding regularly (about once a month), even though it isn't the highest point in the system. The two upright rads...
Replies
35
Views
1K
Oil boiler (now~15 years old) unvented system with 17 radiators. We moved in 5 years ago and I had to keep bleeding the same radiator. The bleed gas could be burned with a blue flame and the water was acidic (pH 5.5). Since then system has been chemically flushed (it was not too bad) and the...
Replies
1
Views
203
I've got a non condensing Glowworm Ultimate with gravity tank and hot Water tank in a 4 bed house. 11 radiators 1 double 1400mm length 1 P+ 1400mm length 2 P+ 400mm length 7 singles 400mm 1 mains shower average water pressure Any recommendations on combi boiler and KW? Boiler budget...
Replies
7
Views
481
Hi, I have just had my central heating system "upgraded" for a four bed-roomed detached house. The heating company recommended going from the open vented system to sealed / pressurized system, new pump ( UPS3 Grundfos ) all new plastic pipework ( extending ) the 22mm feed and return pipes so no...
Replies
9
Views
994
Hi I have a Glow-worm back boiler which is giving me grief (I would have upgraded it by now but its a listed building and there's issues with venting through the external wall and I'm reluctant to go with an electric boiler instead (because of the consumption cost)). It's a sealed system. The...
Replies
6
Views
420
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock