I have a Y-plan system with a Honeywell 4073 three port valve. The valve is several years old.
There is a bypass gate valve across the HW cylinder coil. It is cracked slightly open as it always has been.
The pump has always been on minimum speed and has not been changed.

Since starting to use the heating this year, I often get a loud bang from the 3 port valve when the boiler & pump stop once the room stat reaches temperature. This happens when the valve is in position A i.e. HW is satisfied.
The bang does not happen every time.

My understanding is that the valve should remain in the same position in this situation with port A remaining fully open and the motor stalled.
(Grey wire = ‘ON’, White wire = ‘OFF’).
After the bang, the lever remains free to move over its full range of travel which indicates it is still in the port A open position.

I have also noticed that the pump overrun switches on for a short time after quite a long delay after the boiler has switched off (I would guess after a couple of minutes).

The system was cleaned using Sentinel X400 a few weeks ago. It was left in for a couple of weeks then drained and refilled with water. After running the pump for a while to help flush the system, it was drained again. 1.5L Fernox MB1 inhibitor was added plus 500ml of Sentinel X200 boiler noise reducer.

All the rads and the cylinder coil have been bled several times.

Any idea why I am getting this noise from the valve?
 
I should add that if I switch off the boiler + pump manually via the programmer (shortly before the room stat would have switched it off), then I don't get the bang. It only happens when the boiler + pump is switched off via the room stat.
 

Reply to Three Port Valve bang when heating switches off. in the USA area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
296
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
346
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
198
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock