On an unvented cylinder if the expansion vessel has lost its charge. Can this still be the cause of dripping/discharge from the temperature relief valve. Or if the expansion had lost its charge would it discharge through the pressure relief on the composite valve? Thanks
 
If the expansion vessel had lost its charge I'd expect the expansion relief valve to act first, unless itself was faulty. If the combined temperature and pressure relief is discharging that symbolises other problems. Either can be affected by a number of things. If you're not G3 then best get someone who is to attend.
 
I am g3 yes. I've had it before were the pressure relief on the composite valve has dripped as the expansion has vessel has lost it charge. The expansion has lost it charge its charge on this one. The temperature relief has its own tundish on it and is dripping I cant tell if the pressure relief is dripping too as its combined after the tundish.
 
Is there anyway you can catch the drip from combined temperature and pressure relief and check pipe termination for possible expansion relief drip? Having said that that is installed wrong and both need to terminate into D1 of tundish.
 
Is there anyway you can catch the drip from combined temperature and pressure relief and check pipe termination for possible expansion relief drip? Having said that that is installed wrong and both need to terminate into D1 of tundish.
Yes I release it is installed wrong. I will recharge the expansion vessel before I go any further.
 
If the vessel had lost its charge, too much charge or failed altogether, or the pressure reducing valve had failed or not present then the expansion relief valve SHOULD drip first as its pressure setting is usually 1 bar lower than the combined pressure and temperature relief valve. The only time I would expect the combined pressure and temperature relief valve to activate due to excess pressure is if there's a problem with one of the above and the expansion relief valve had failed.

Edit: If there was a problem with a mixer unit letting by then any cold mains pressure not balanced and at higher pressure than supply to cylinder can also cause this problem.
 
Last edited:
If one uses the balanced supply and there is a problem meaning the valve to the unvented needs to be shut off - the property loses all water. Is this a usual scenario?
 
If the vessel had lost its charge, too much charge or failed altogether, or the pressure reducing valve had failed or not present then the expansion relief valve SHOULD drip first as its pressure setting is usually 1 bar lower than the combined pressure and temperature relief valve. The only time I would expect the combined pressure and temperature relief valve to activate due to excess pressure is if there's a problem with one of the above and the expansion relief valve had failed.

Edit: If there was a problem with a mixer unit letting by then any cold mains pressure not balanced and at higher pressure than supply to cylinder can also cause this problem.
In my experience the T&P always drips when expansion has failed. Agreed in theory the PRV at 6/7 should activate first, however from what I have seen they don’t. You also have to remember the T&P only start dripping, not discharging. They can start dripping at 6/7 bar before their set point.
 
If one uses the balanced supply and there is a problem meaning the valve to the unvented needs to be shut off - the property loses all water. Is this a usual scenario?
The one I'm looking at just has the balanced cold caped on the composite valve. I'm not sure if there's another pressure reducing valve on the mains. So back pressure could be an issue too I guess.
 

Reply to Temperature relief valve dripping in the USA area at PlumbersForums.net

Similar plumbing topics

Hi. I need a new toilet supply line but don’t know the size type of the fitting at the shut off valve. It is not 3/8 compression. It is a plastic nut about the same size as the one going into the cistern but has a different thread. Attached is a photo. Can you advise. Thanks.
Replies
2
Views
167
Recently had a Viessmann Vitodens combi boiler installed, quite often when the adjacent cold mixer tap is opened the boiler starts for a few seconds! Can anyone tell me what is causing this? And how to cure?
Replies
3
Views
181
I have a plumber coming tomorrow to change a cartridge on a badly dripping tap on my bathroom mixer unit. There is no separate isolating valve for this tap so I'll have to close the stopcock. I tried closing it today but it won't go absolutely 100% closed and there is still a very slight flow...
Replies
1
Views
212
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
150
Our kitchen mixer tap has started dripping. Like so much of the plumbing in our almost new build bungalow, it is lacking! The plumber didn't install any isolating cocks in the H&C feed to the tap so how can I identify which of the valves is passing? Shut the whole H&C water system down?
Replies
7
Views
189
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock