Boiler was serviced 2 months ago by Vaillant . Timer /control seems fine. Thermostat looks less than 3 years old .Timer turns off heating /water at 10pm due back on at 5 am . Friend woken up by warmth from rads .All rads too hot to touch almost .



where could the issue be ? cheers
 
Do you have a hot water cylinder?

Is the programmer set to reheat the hot water cylinder during the night?

Do you have a single '3-port / Y-plan' valve that controls where the flow from the boiler goes or two (or more) '2-port / S-plan' valves?

Which model boiler do you have?
 
The control could be faulty .org the microswitch inside the motorised valve can get stuck. The microswitch is what brings the boiler on when motorised valves are installed, as they have a permanent live and switch live (switched via the microswitch).
 
Top one was changed 3 months ago.
 