Hi folks - nice to join this forum and I wish I'd done so earlier. Some urgent advice needed please..

Our plumber has had to repipe the central heating in our Victorian house because the existing system was single pipe. He has done this using plastic pipe and push fittings. The first time we turned the heating on, the ground floor system leaked into the underfloor void at a sagging 90 degree joint that sits in the middle of circa 4 metres of unsupported pipe. I've attached a video which shows exactly what this looks like..

I'm not convinced by his argument that the pipes don't need any support and only the fitting is at fault, so to save me the roundabout discussion could anyone please point me to the relevant guidance that defines how much sag is acceptable and what the support criteria is or isn't for 22mm plastic pipe?
 

Attachments

  • IMG_2111.mov
    60.9 MB
Needs clips every meter and lagging
 
Hi folks - nice to join this forum and I wish I'd done so earlier. Some urgent advice needed please..

Our plumber has had to repipe the central heating in our Victorian house because the existing system was single pipe. He has done this using plastic pipe and push fittings. The first time we turned the heating on, the ground floor system leaked into the underfloor void at a sagging 90 degree joint that sits in the middle of circa 4 metres of unsupported pipe. I've attached a video which shows exactly what this looks like..

I'm not convinced by his argument that the pipes d5on't need any support and only the fitting is at fault, so to save me the roundabout discussion could anyone please point me to the relevant guidance that defines how much sag is acceptable and what the support criteria is or isn't for 22mm plastic pipe?

No sag is acceptable the lazy scrot, should be clipped every 0.5m minimum for horizontal run in 22mm.

See page 19.
 
Last edited:
...and btw the fitting isn't necessary leaking because it's faulty. It's more likely to be leaking because the pipe isn't properly seated and or the fitting is under stress because of the lack of support.
 
Needs clips every meter and lagging

agreed about the lagging -
No sag is acceptable the lazy scrot, should be clipped every 0.5m minimum for horizontal run in 22mm.

See page 19.

Perfect, thanks! I’m using a registered gas engineer so never expected this :(

Besides the manufacturer‘s spec, what / where are the building or other regs that installers should be following?

also, from a trade perspective, what is a customer’s recourse when work doesn’t meet regs or standard? It strikes me that a lot of work could / should be checked by an independent, or at least recorded as proof of continuing competence.
[automerge]1604740603[/automerge]
...and btw the fitting isn't necessary leaking because it's faulty. It's more likely to be leaking because the pipe isn't properly seated and or the fitting is under stress because of the lack of support.

totally agreed, and also, no idea how my plumber expects to be able to drain the ground floor.

it gets worse really as I removed the floorboards and can see that other (15mm) pipe is only supported by a partition wall and - no kidding - an electric cable.. see attached pic.
 

Attachments

  • 8CFC6976-7114-4C1E-B849-1BAB823CD86E.jpeg
    8CFC6976-7114-4C1E-B849-1BAB823CD86E.jpeg
    130.7 KB · Views: 17
Last edited:
No pipe lagging under a floor void big no needs insulating

sorry, do you mean it does or does not?

The pipes are feeding three radiators, each 1.5kW, so I can see the case that at max demand the flow is high enough that piping heat loss is relatively low, but at lower flow does insulation make that much difference?
 
British Standards BS6700:2006
Design, installation, testing and maintenance of services supplying water for domestic use within buildings and their curtilages.

Maximum spacing of fixing for internal piping

PB or PEX pipe

clip spacing = horizontal/vertical

Up to 16mm diameter = 0.3m/0.5m
18 to 25mm diameter = 0.5m/0.8m
 
Last edited:

Reply to Supporting pipes under floorboards + insulation in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
165
Copper pipes, I think its fair to say, is not what it used to be, the copper is getting thin while the cost is going up. Meanwhile, plastic Pushfit seems to be getting better and better, cost and convenience was always better, but now the quality is to, have we reached a stage where plastic will...
Replies
2
Views
221
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
202
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
198
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
297
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock