Hi,

I'm doing a bathroom refurb and wanting to move both the WC and wash basin over to the right.

In the picture attached, green is how I think I should position the new WC and orange is how I think I should position the new wash basin.

I know that the waste pips should have a slope between 1:40 and 1:110, my question: can a waste pipe have a vertical drop of any height and then be connected horizontally to the branch stack at the right slope?

The previous plumber did this with wash basin waste pipe like in the picture... and yes he also didn't secure it and he didn't put a cover on the top of the branch stack, so I don't know if what he did is correct.

You don't have permission to view attachments. Attachments are hidden.
 

Attachments

    You don't have permission to view attachments. Attachments are hidden.

Undertrained

Plumber
Gas Engineer
Messages
760
Solutions
1
Green one might not work, as you’re showing it where the wc connection is. I don’t know what cover you’re referring to either.
 

Ric2013

Plumber
Messages
3,329
Waste pipe branches are generally 1:11 to 1:55 (18 to 90mm fall per m run) - source: ADH. Where did you get your figures of 1:40 and 1:110 from?

Use 40mm (1.5") pipe (minimum) for your washbasin as it looks like the run is around 3m.

Yes, your plumber did not put a bird cap on the soil and vent. Realistically there must be millions installed without yet birds nesting on them is not a frequent event. Not clipping the basin waste branch is a bit silly though!
 
Messages
2
Waste pipe branches are generally 1:11 to 1:55 (18 to 90mm fall per m run) - source: ADH. Where did you get your figures of 1:40 and 1:110 from?

Use 40mm (1.5") pipe (minimum) for your washbasin as it looks like the run is around 3m.

Yes, your plumber did not put a bird cap on the soil and vent. Realistically there must be millions installed without yet birds nesting on them is not a frequent event. Not clipping the basin waste branch is a bit silly though!


The falls for waste pipes is a figure I got from this chap on youtube:




He made his soil waste fall just under 1:110, which you can see at the 9 minute mark.

I'm unfirmiliar with ADH but I did some further digging and found a source that confirms 18-90:1000 fall for waste pipes. Thanks for the correction.

You don't have permission to view attachments. Attachments are hidden.
 

Attachments

    You don't have permission to view attachments. Attachments are hidden.

Ric2013

Plumber
Messages
3,329
ADH is the Approved Document (for the Building Regulations Part) H and shows a tried and trusted and legally accepted way of meeting the requirements - this does not mean you cannot meet the requirements in other ways, but it is what we generally go by and by and large says the same thing as the source you have looked at. You won't go far wrong with Treloar anyway.
 

Reply to slope question about relocating WC soil pipe in the DIY Plumbing Forum area at PlumbersForums.net

Similar threads

O
I am refurbishing a bathroom and adjoining en-suite which back onto each other and are on the first floor of the house. Both have a toilet, washbasin and shower. The showers are electric and the flow rates are not excessive. There is a straight horizontal soil pipe (with appropriate slope 1:40)...
Replies
3
Views
808
Timmy D
T
S
Hi, I'm a Gas Engineer currently renovating my new house. I'm not too clued up on running waste, soil stacks etc so looking for a bit of advice We had an existing 3 1/2 inch waste pipe running out the back. We are extending out to the back now and have cut the pipe down. Stepped it upto 4 inch...
Replies
3
Views
397
SA7426
S
S
Im installing a wall hung toilet frame and just working out where everything needs to be positioned etc. I want to move the frame/toilet over to the right as far as possible but can anyone tell me if there is a minimum distance that should be used for a straight run before going into the...
Replies
3
Views
4
ShaunCorbs
ShaunCorbs
H
Hello, I would very much appreciate some help/feedback on what I am proposing for my very small ensuite bathroom. While refurbishing it I’m proposing to add a shower. It’s just 1.2m x 1.6m. I have seen similar posts to this on the forum but not quite my situation. I am proposing to run one...
Replies
1
Views
734
PETE 123
P
J
The basin waste runs horizontally for about 2m in 32mm and the bath waste runs for about 1m before they meet and tee together. From the tee the waste pipe runs horizontally for about 2m in 40mm to the soil stack. If you look at the pic the top pipe with the level on is 40mm bath waste and the...
Replies
6
Views
699
Ric2013
R

Newest Threads (Please Reply)

Search Forum

Top