Hi I am trying to figure out my bathroom sink waste problem
Renovating the bathroom and the wife wants the sink the opposite side of the room. The stack is in the opposite corner the only way I can get to it is through 2 joists that have already been cut for the old shower waste.
If I do this my sink waste will be in an L shape, from the stack to the first bend I have a fall of over 100:1 it is around 1m long then an elbow joint. Along the joist From the elbow joint to where the pipe will need to come vertical through the floorboards (around another metre) there is hardly any fall.

Would this work ok or should I look to get a pump?
I really dont want to drill any more holes through the joists. Green i can get a fall. Red is where it is almost level
20210307_165012.jpg
 
15mm a meter min

the notches in the joists look deep max you can do is 1/8th of the depth
 
How much fall do you have ?
 
How much fall do you have ?
The pipe along the green line falls just short of 1.5cm between the elbow and second joist. I will need to put a bend in to make a steeper drop to get it to the stack. The pipe along the red line there is barely any fall.

If the notch by the 2 standing screws is 1/8, you must have a 50cm tall joist there!
Yea sorry, this one is more like 1/4. These cuts are from the old shower waste that I took out. These were done by the builder who made the extension! This is why I am not keen in making any further holes in the joists.
Whoever built the extension to our house needs shooting, found some shocking things
 
May I suggest any bend, especially under the floor, should be a swept bend rather than a knuckle bend (look up these two terms on any web browser for pictures)?
 
Last edited:
May I suggest any bend, especially under the floor, should be a swept bend rather than a knuckle bend (look up these two terms on any web browser for pictures)?
Thanks for the comment but doesn't really answer my OP.

No one got any advice if this pipework would be ok if a pump was installed on the waste?
 
Thanks for the comment but doesn't really answer my OP.

No one got any advice if this pipework would be ok if a pump was installed on the waste?
If you fit a waste pump, I think you can use 22mm pipework and can even run with a negative fall. You'll need to check manufacturer's installation instructions for the pump. I think the feeling may just be that a pump is a last resort.

Personally, if that is in your own house, I suppose my thinking is that, so long as that waste pipe is going to be accessible and you aren't about to tile over the floor, I would consider using your proposed run with minimal fall, supporting the pipe every 50cm, upgrading the waste to 40 or 50mm (1.5" or 2") instead of the presumably 32mm or 1.25" you currently have if you can, sweeping the bends, and deburring all cut tube meticulously. You may find that while it does not meet the recommendations of the building regulations Approved Documents, it may still work perfectly well.

This wouldn't be best practice and it's a risk, but, if it doesn't work, then you haven't wasted much money and can then go on to fit a pump. Personally, I would find a way of making the pipe have 15mm per m drop or relocate the basin as I'm a plumber, but, in fairness, a study of old sewers run at varying drops did not show increased incidence of blockage even at drops of less than 1:1000 and a washbasin is unlikely to overload a short length of 2" pipe to the point that it is running full bore, even if laid almost level. This is why I think you might get away with it.
 
If you fitted a pump you would redo that run entirely. I.e. not use what you've got. Look up saniflo 10 golden rules. Pumps pump up, not down. At least then you could brace the joists
 

Reply to Sink basin waste fall advice in the USA area at PlumbersForums.net

Similar plumbing topics

Hi all, Desperately in need of help. Getting very annoyed with myself Replaced the click plug in my bathroom for a new Basin Slotted one along with the Thomas Dudley Basin Waste kit All relatively straightforward to put together but why is it still dripping I'm using the preexisting metal...
Replies
5
Views
352
Hi, I need some advice connecting my bowl sink to the waste. There was a Insinkerator installed that I have replaced with basket strainer waste (Viva PP0011). I need to connect the waste but I find myself going around in circles in regards to selecting the correct parts. Thanks FrankW
Replies
10
Views
781
Hi guys first post. I am in the process of rejuvenating a double wash sink. It was needing the waste below looked at for a washing machine and dryer, as it had a sunken elbow and unbeknownst it was a mix of 1 1/4 and 1 1/2, including the sink wastes themselves. I bought new matching 1 1/2...
Replies
3
Views
330
Attached is a ground floor picture of the soil pipe in our home. There was originally a toilet which has now been permanently capped off and you can also see a sink waste pipe attached. My plan is to drill out one of the 50mm sockets directly opposite the current sink waste for a new 40mm...
Replies
4
Views
1K
My bathroom Basin was installed some years ago by a professional plumber. For whatever reason, the waste was fitted using silicone rather than plumber’s mate. The floor was originally tiled, but I replaced it with high quality vinyl, when fractures began to appear in the grout. As part of this...
Replies
2
Views
398
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock