I have two showers at first floor level fed by a Worcester Combi boiler. Both showers are Mira Agile thermostatic mixer showers and are fed from the same hot and cold supply runs. One shower has been in for approx 2 years and at the moment is working fine. I had temperature fluctuation problems with the other (which has been installed for about 4 years) about 8 months ago and replaced the cartridge and the filters. At first the new cartridge did the trick, but I'm getting the same temperature problems again now, and I notice the boiler is cycling as the shower temperature goes up and down. As the newer shower is working ok I assume the problem is not with the boiler. I am wondering if the replacement cartridge is the culprit? Any thoughts/ other suggestions would be appreciated. Many thanks.
 
Check that the shower is plumbed in correctly, i.e. hot water is going into the correct inlet. If the ports are reversed the temperature setting will be very sensitive and will tend to swing between extremes of hot and cold.

If it's not this, the next most likely cause is insufficient flow causing the boiler to cycle. Set the the flow rate by timing how long it takes to fill a jug or small bucket.

If plumbing is okay and flow rate is consistent and within spec, then I'd suspect the cartridge.
 
Check that the shower is plumbed in correctly, i.e. hot water is going into the correct inlet. If the ports are reversed the temperature setting will be very sensitive and will tend to swing between extremes of hot and cold.

If it's not this, the next most likely cause is insufficient flow causing the boiler to cycle. Set the the flow rate by timing how long it takes to fill a jug or small bucket.

If plumbing is okay and flow rate is consistent and within spec, then I'd suspect the cartridge.
Thanks, Chuck
The pipework is plumbed in ok, and the flow rate when I turn full on is good (although the temp is cold until I reduce the flow considerably). I will double check the flow rate however as you suggest. If all checks out would seem to be the cartridge then. This will be the third cartridge for this shower -is there anything that can cause cartridges to wear out sooner than they should?
 
This will be the third cartridge for this shower -is there anything that can cause cartridges to wear out sooner than they should?
If replacing the cartridge fixes the problem, you should be able to return the one that failed after 8 months under warranty.

Did you replace the original with a 'genuine' Mira part from an authorised stockist or some cheaper 'equivalent' from eBay? Is your water very hard, or acidic, or from a private source? Did you flush the pipes to ensure there was no grit or blockage before installing?
 
If replacing the cartridge fixes the problem, you should be able to return the one that failed after 8 months under warranty.

Did you replace the original with a 'genuine' Mira part from an authorised stockist or some cheaper 'equivalent' from eBay? Is your water very hard, or acidic, or from a private source? Did you flush the pipes to ensure there was no grit or blockage before installing?
I got the replacement cartridge from MIRA, so it should have been ok. The water is quite hard where we are, but I have a softener, and the other shower doesn't seem to be affected. Yes the pipes were well flushed before fixing the shower mixer. I have made contact with MIRA re the situation and am awaiting their reply. I'll let you know how I get on...
 

Reply to Shower temperature problem in the USA area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
300
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new brackets, dismantle that existing one and start again or I could try and re attach via those screws, removing the broken ones from the plate and wall...
Replies
1
Views
170
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
6
Views
143
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
228
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
205
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock