Hi -

I had an old watermill low viltage pump that worked great for years. That went so replaced with a new (Grundfos- positive head) from my hot water cylinder. All it does is power my bath/ shower (via one mixer tap).

The issue is that since installation it starts up on its own (without the tap being opened) most mornings (and intermittently throughout the day), making a whirring noise sounds like squeaky air being released.

I have just discovered that the mixer tap (to the bath/shower) is in fact dripping.....The plumber is suggesting that this is the cause so I am changing the tap but will this solve he problem?
 
Are you sure its positive head as these use the flow switches to start & stop them and require ~ 0.5 to 1 LPM to switch, a drip will hardly start it. A negative head pump or universal uses a pressure switch and a drip will certainly start that.
 
Thank you. That's reasssuring.
Are you sure its positive head as these use the flow switches to start & stop them and require ~ 0.5 to 1 LPM to switch, a drip will hardly start it. A negative head pump or universal uses a pressure switch and a drip will certainly start that.
Hi - Thats what I thought.... Its definitely a positive head. Its in a flat - hot water cylinder in cupboard (which plumber also says is too small)

The plumber who fitted the new pump..came back and discovered that he tap was dripping (it is I've seen the video- which unfortunately IT issues mean I cant attach..) ......his view is that the change in pressure due to the leak is starting the pump off.......and Im not convinced but guess I wont know until mixer tap is changed....
 
Can you measure the drip into a bucket for 30 secs or so to give you a flow rate.

Edit: what stops the pump, once the drip has started it?.
 
Can you measure the drip into a bucket for 30 secs or so to give you a flow rate.

Edit: what stops the pump, once the drip has started it?.
Hi- unfortunately not as not there...rented..

sometimes there is a drilling sound first but then the whining/squeaky noise.... and then it stops of its own accord.

Thank you
 
Bit strange, both would normally be fed from the same head, the CWST to the cold end and the CWST to the hot end via the HW cylinder, something seems to be moving one of the flow switch floats hi and then low enough to stop/start the pump. Assuming no flow switch problems then just possibly a air pocket building up/collapsing somewhere (hot side?) but this would point to improper installation. Presume hot water temperature not exceeding 60/65C.
 
Are you sure it isn’t also connected to a lavatory?
If a flushval e let’s by (very common) , the inlet valve will open to make up volume- this could trigger the pump.
 
Thanks Ben but plumber tells me the pump has its own dedicated feed....and the noise happens early morning before (the only person who lives there) is up and about. Plumber reckons its something like as the pressure is highest in the mornings the drip sets it off then...I'm just hoping replacing the (dripping) mixer tap help.s..
 
Ben May be suggesting that the toilet cistern is supplied from the pump cold end discharge I think.

Only way high pressure/more drips in morning is possible is that the mains is connected to the cold end inlet? Except that the header tank is at a higher level
 
Flush the toilet, see if the pump starts.

Isolate either the hot or cold inlet at the pump valves over night and see if it resolves the issue. This will focus the fault find on the correct supply.
 

Reply to Shower Pump Starts on its own intermittently in the USA area at PlumbersForums.net

Similar plumbing topics

We have a gravity fed hot water system in our the house we have just recently moved into. It works fine with the downstairs shower, however we are about to upgrade the upstairs bathroom and are considering installing a shower bath. My concern is that although there is more than sufficient...
Replies
15
Views
651
A
Hey, here goes and I hope it works.. never used one of these before! I have a Sagittarius Ergo mixer shower min bar of pressure required 1 bar. Connect to this is a 1.5 bar Ora Salamander pump for a positive head, this was connected by a plumber of course and we’ve had it all rigged up...
Replies
1
Views
400
About 9 months now, started suffering intermittent but frequent hydraulic shock thwacks, sometimes very violent, below Harvey's water softener in mains cold copper pipe. So far, water tank ballcock replaced, kitchen mixer tap replaced, Harvey's serviced the water softener, approx. 5 years old...
Replies
0
Views
401
Good Afternoon all, I am hopeful someone may be able to offer some guidance on the following. In the home we have a gas boiler (serviced annually, October time) providing hot water to the CH system which is split into 3 zones (Honeywell 2-way valves) and it also heats the HW tank (Tribune...
Replies
5
Views
479
Hello all, So been having somewhat of a time with my Aqualisa Quartz 9.5 electric shower. A few.month ago I put up with a few problems it was having and in the end I replaced everything, new engine and new front cover . This was working great for a month or so, but now noticed an intermittent...
Replies
6
Views
423
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock