I would be getting them back in. You don’t just switch this stuff on. Needs commissioning properly.
 

Gasmk1

GSR
Messages
1,139
Reaction score
327
Thank you. One quick thing. Isn't 65 dc the input temperature (from the boiler) and 53 the temp going into the floor? Am I mis-reading things? (Of course, 53 dc may well still be too hot). Thanks again!
65 dgrees C is the input temp 53 degrees is the return temp afte rgiving heat up so its way too hot on th e flow as mentioned to you, all needs setting up properly
 
OP
M

Mr S

New Member
Messages
21
Reaction score
2
All.

Thank you for your recent advice re the temperature of my UFH; it was invaluable.

Hoping for a second go.

Our plumber returned the other day and finally - so he assured us - properly commissioned the UFH. We have noticed on more than one occasion that when we try to run UFH to multiple rooms the Manifold makes a VERY loud singing noise. (I say "singing" as it's quite a high pitched hum, more like an old-school kettle boiling).

What can be causing this and what is the best way to stop this happening? Is this related to the flow rates not being properly set (despite assurances related to this)?

Many thanks (again), Steve.
 

Chalked

Plumber
GSR
Messages
4,935
Reaction score
2,280
All.

Thank you for your recent advice re the temperature of my UFH; it was invaluable.

Hoping for a second go.

Our plumber returned the other day and finally - so he assured us - properly commissioned the UFH. We have noticed on more than one occasion that when we try to run UFH to multiple rooms the Manifold makes a VERY loud singing noise. (I say "singing" as it's quite a high pitched hum, more like an old-school kettle boiling).

What can be causing this and what is the best way to stop this happening? Is this related to the flow rates not being properly set (despite assurances related to this)?

Many thanks (again), Steve.
Hi yes that is down to a incorrectly set up system . The noise is the mixer valove struggling to control temps when the flow rate and return temp is too high.
Needs setting at 47 degrees and then each loop needs to have a 7 degree differce.
I’ve also had the same noise on a faulty mixer too.

Can you post a pic of the manifold as it is set right now?
 
OP
M

Mr S

New Member
Messages
21
Reaction score
2
Hi yes that is down to a incorrectly set up system . The noise is the mixer valove struggling to control temps when the flow rate and return temp is too high.
Needs setting at 47 degrees and then each loop needs to have a 7 degree differce.
I’ve also had the same noise on a faulty mixer too.

Can you post a pic of the manifold as it is set right now?
Hi. Thanks for your help. Sorry - I didn't see you reply until now.

After speaking with the manufacturer - Wunda - last week I managed to make some progress with the noise by reducing the pump speed to setting "2" (the recommended speed for 7-port manifolds).

However. There is still some occasional noise and I suspect it's down to what you say. I also reduced the outlet temperature down to the minimum (40 deg) in order not to damage the LVT even further, so it's interesting you're suggesting 47 deg. I know the loop temperature can be reduced further by changing the flow rates, but I didn't think it was so significant.

Any advice is very welcome. Thank you.

IMG_2763 (1).jpg

IMG_2762 (1).jpg

IMG_2765 (1).jpg

IMG_2764 (1).jpg
 
OP
M

Mr S

New Member
Messages
21
Reaction score
2
Hi yes that is down to a incorrectly set up system . The noise is the mixer valove struggling to control temps when the flow rate and return temp is too high.
Needs setting at 47 degrees and then each loop needs to have a 7 degree differce.
I’ve also had the same noise on a faulty mixer too.

Can you post a pic of the manifold as it is set right now?
Hi. Further to the above.

I should add that we have two separate flooring types - porcelain tiles (with scree) plus LVT (overfloor with s/l compound). Unsurprisingly I'm having trouble getting the temps in the rooms with porcelain times sufficiently warm given I need to keep the temp low for the LVT.

I'm beginning to think I need two separate manifolds, given the need for a 10 degree difference in outlet temp? I wondered if you agree?

Many thanks again, Steve.
 

Ric2013

Plumber
Messages
2,013
Reaction score
465
Thank you. One quick thing. Isn't 65 dc the input temperature (from the boiler) and 53 the temp going into the floor? Am I mis-reading things? (Of course, 53 dc may well still be too hot). Thanks again!
No. That's the temperature of the water from the pump, which should be a mixture of hot boiler water and cooler water that has already made a circuit of the UFH.
 

Forum Sponsors

Corgi - Plumbing Supplies for Professional Plumbers - Plumb Advice

Plumbase - Plumbing Parts for Plumbers - Plumbers Advice

Power Shower Booster for Power Showers - Plumbing Advice

Underflor Heating Systems by uHeat - Plumbing Advice

Wetroom Supplies by Wetroom Store

Nicobond - Wetroom and Tiling Supplies - Plumbers Installation Advice

Corgi - Plumbing Supplies for Professional Plumbers - Advice for Plumbers

Do you have a DAB radio for work?

  • Yes

  • No


Results are only viewable after voting.

Latest Plumbing Advice

Top Bottom