Whether it be the usual gate valve or the more correct lockshield valve.

Jennie raised a point elsewhere on this forum and someone mentioned the purpose of these being 'by reducing the flow, the coil will remain hotter longer. Thus heating the water quicker'.

Makes no sense to me as reducing the flow would surely reduce the average temperature of the coil. I'd have thought the maximum heat transfer would happen when the average temperature of the coil was as high as possible, hence better to leave the valve fully. Great on a W plan.

But on a Y plan, that would rob flow from radiators and unbalance the system, so I'd aim at having the same temperature drop across the coil (with the cylinder cold) as across each radiator. As the cylinder heats up, the temperature drop across the coil will reduce to very little, but you need a high coil temperature to get the secondary water to 60°C without excessive boiler cycling, so I suspect the setting should be carried out with a cold cylinder.

But this is just my opinion. Any thoughts?
 
I always thought the only reason for them was to restrict flow through the cylinder to allow more flow through the radiators. Never considered it an option of keeping heat in the coil because as you say, that makes no sense.
 
Last edited by a moderator:
But on a Y plan, that would rob flow from radiators and unbalance the system
Agreed, I've never seen much advantage in a mid-position valve, as if the cylinder only is heating, and then CH calls, there is cold water through the coil for a while and cylinder temperature likely to fall. Maybe not recover till CH is satisfied, specially if the rads are generously sized to help condensing. Throttling the coil flow might help, but as you say, that would reduce the heat transfer when HW only is calling.
 

Reply to Setting up a balancing valve on a cylinder coil on Y plan? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I'm looking to purchase a 300L unvented indirect cylinder to work with a standard heat only boiler. I may have solar panels in the future, but likely the PV kind rather than the thermal kind, and won't be having heat pump in the future. So the cylinder would be connected to the boiler at...
Replies
9
Views
640
Hello, my HW is taking longer than expected to heat up and it's getting worse. I can go 10-40 degs after 1.5 hours of only heating HW, whereas I should be going 10-60 degs in 30-40 mins by my maths. Don't even mention trying to heat HW and CH at the same time. 30 mins with the immersion adds...
Replies
2
Views
377
Does anyone know of a weather compensation unit that can be fitted to a cylinder? I have an Ideal Logic Max H24 which heats a thermal store. The boiler can take an Ideal weather compensation unit to raise the target flow temperature as the outside temperature drops, but the store temperature...
Replies
0
Views
359
Hi all, so things are coming on now at last! New 250 cylinder in loft all pretty much plumbed in. F+E tank binned off, new ups pump, 2 new zone valves imstalled... Now im up to wiring up, have done the immersion, so we have hot water, ive wired in the dual stat. I have me head roughly into what...
Replies
58
Views
3K
Hi everyone, Is this set up correct: Attic stop valve turns off the cold water to my bathroom (I think it is the rising main in the attic which I and other residents in the building share as we have shared supply to bathrooms and kitchens) Under kitchen sink stop valve turns off cold water in...
Replies
0
Views
489
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock