I have a Riello RDB Burner housed within a Grant Outdoor module 70/90. During the last 2 months the boiler has stopped firing up at about 3 week intervals and I have had to clean the photocell in order to rectify the problem. I had the boiler serviced last summer.
 
If you're having to clean photocell due to sooting up frequently then obviously it's not burning cleanly. What did the service engineer do? Did he replace nozzle? Did he adjust pump pressure? Did he even use a smoke pump and flue gas analyser? It could be a number of things he did or didn't do, plus other problems that have arrived since
 
If you're having to clean photocell due to sooting up frequently then obviously it's not burning cleanly. What did the service engineer do? Did he replace nozzle? Did he adjust pump pressure? Did he even use a smoke pump and flue gas analyser? It could be a number of things he did or didn't do, plus other problems that have arrived since
he possibly did all those things last summer that is approx 7 months ago or longer so something may have happened since then
 
he possibly did all those things last summer that is approx 7 months ago or longer so something may have happened since then

We don't know how competent the engineer was though do we. You have to be qualified to touch gas but anyone can touch an oil boiler so we don't know what the engineer did or didn't do. It could as we both said be a recent problem, which could be a number of things.
What ever issue this requires someone who knows what they're doing with the right equipment.
 
If you're having to clean photocell due to sooting up frequently then obviously it's not burning cleanly. What did the service engineer do? Did he replace nozzle? Did he adjust pump pressure? Did he even use a smoke pump and flue gas analyser? It could be a number of things he did or didn't do, plus other problems that have arrived since
Thank you for this detailed and helpful response. I can now approach the engineer with some better informed questions.
 
Thank you for this detailed and helpful response. I can now approach the engineer with some better informed questions.

You need to call back your engineer and get him to service it and go over it again. It could be as simple as a worn nozzle or dirty fan impeller causing sooting up over time. The sooting up could also be caused by a number of problems, I'm not going to rattle them all off, if he knows what hes doing then he should find the fault, its basic combustion laws to be honest.
 
If its sooting at the photocall it could be an indication of struggling to get flue gases away.

Time to get the pro back. Sooner rather than later.
 

Reply to Riello RDB Burner Photocell Sooting Up in the USA area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
289
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
208
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
346
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
4
Views
201
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
6
Views
134
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock