Increase their impedance, i.e. restrict them by partially closing their lockshield valves.What does "throttle the returns" refer to please?
It means shutting in the rad return valves (a form of balancing) or to get a quick and easy feel of what can be achieved, just throttle the pump suction valve or preferably a common return valve from "all" the rads.
Room thermostats for use with gas boilers are typically limited to a maximum of 6 on-off cycles per hour, for oil boilers this should be changed to 3 per hour. The boilers themselves will usually have their own short-cycle prevention controls built-in.When considering boiler cycling am I correct in thinking this is the total number of times the boiler turns on and off inside an hour of average running? Or how is boiler Cycling assessed in your opinions? For example at present the boiler must be firing up again about 16 times per hour. If a nozzle downsize reduced that to 10 or less then is that an indicator of a more suitable / efficient boiler size?
So the Delta temperature makes perfect sense there. It is a great influence on the heat output of the radiator. The LPM flow is calculated by the delta temp and rad size(?)This is a screenshot of the old spreadsheet that I do the calcs on and contains more info.
You don't have permission to view attachments. Attachments are hidden.
When downstairs is on again tomorrow I could partially close one of the ball valves on the mag filter at return line would that have same effect? Just to test temporarily. Or better to turn down the gate valve on the pump inlet instead?
I do think the boiler is oversized really. I am interested to take all readings including the hour counter measurements and compare before and after nozzle downsize.
Aka to use 2no hour counters. 0.01 hr accuracy. One connected to the circulator pump which represents the heating flow / duty time and the second to a 240v circuit on the burner. May try to measure actual nozzle firing time VS just when the boiler stat is calling.
When considering boiler cycling am I correct in thinking this is the total number of times the boiler turns on and off inside an hour of average running? Or how is boiler Cycling assessed in your opinions? For example at present the boiler must be firing up again about 16 - 20 times per hour. If a nozzle downsize reduced that to 10 or less then is that an indicator of a more suitable / efficient boiler size?
That's it, the rad size is in Kw, I just used 1kw, the flowrates are then pro rata for other outputs.So the Delta temperature makes perfect sense there. It is a great influence on the heat output of the radiator. The LPM flow is calculated by the delta temp and rad size(?)
That's it, the rad size is in Kw, I just used 1kw, the flowrates are then pro rata for other outputs.
Your pump is definitely oversized, a normal 7M pump would have done the job IMO, the old pump was knackered I'd say.
The ads are fabulous, did you know that ear wax can make you deaf?
Interesting thread. This is the kind of investigative spirit we need to have if we're really to make meaningful improvements to heating systems.
Re the infra-red thermometer, I find they work really well. However, they are usually geared to high-emissivity surfaces (it should normally explain that in the destructions). As such, any reasonably shiny metallic surface can't really be read accurately as it is a low-emissivity surface. However, there is an easy fix in that a piece of masking tape on the pipe can be used as a reliable test point.
I'm not sure re Firebird condensate trap but some traps, to avoid the waste pipe freezing up, fill up the trap with condensate and then blows this down and refills again so on the off chance that this is occuring keep a eye on it but I wouldn't hold my breath as firebird supplied a plastic trap originally which used to melt.
I am going to carry out a test on just one rad soon because as you say, the only sort of fit is if the flow temperature falls as well, see below. I'm quite happy that I had a flow rate of 5LPM both by throttling the 5M pump setting to replicate yours and then at a pump head of ~ 3m unthrottled to give me the same 5LPM. As the boiler output was fairly constant (cycling) at 45 to 50% then the only scenarios that sort of fit are the last two below, ie a flow temp of 64C & return of 35C for 50% output and 45% output at 60C/34C, I didn't see my return going below 42/43C, the only explanation I can give for a apparent low flow temp is that a oil fired boiler acts as a 20/25 litre buffer tank and with the burner off perhaps cold return water flows from the flow side until the burner "catches up" and reheats the buffer??.
You don't have permission to view attachments. Attachments are hidden.
Carried out the TRV test on one X 1.7kw rad and as expected, the TRV was just copening/closing but keeping fairly tight control of the mean rad temp at ~ 42/44C which gave the required rad output of 0.6kw to maintain a room temperature of 20/22C. The boiler had very long cycling times of around 2.5 mins on and 35 minutes or more off. I then progressively introduced the remaining rads (all TRVd) and their mean rad temps reflected the outputs required, the combined return temp didn't vary hugely ~ 39/45C.
Its very difficult to get a good reading in the heat pac due to restricted space but initially it actually seems to rise a little but I suspect this is because the boiler flow pipe turns down immediately where as the boiler return goes out the side of the boiler and then very gradually rises so I think the boiler contents are inclined to "circulate" back through the return. The cycling time matches ~ the rad heat demand but its not that simple as the boiler once it cuts back in when the stat reaches ~ 60/65C has to reheat say 20/25 litres of boiler water from ~ 40c to its cut out of 70C so requires ~ 0.9kwh which takes ~ 2.7 minutes from a 20kw boiler. In general, once other rads are brought back on line then the % firing time does reflect the heat demand.
What are the dimensions of the kitchen rad and is it a double or single?.
Try with the pump speed on two instead of one
Tbh doesn’t really matter temp as that’s not a limiting factor
And tbh if your trying to balance it needs to be on the return as your throttling flow else