You say it's both burners that lockout? Chucking parts at a problem in the hope to fix it is not a good idea and can be costly, especially if you're doing it for two burners at once.
I agree, but I'm at a loss as what to try next, any suggestions thanks
 
I agree, but I'm at a loss as what to try next, any suggestions thanks
The fault sequence is loss of flame signal according to the manual. Steady red for 10 secs 1 short flash 4 long flashes then repeated, so we just press the reset button and it fires up. It's more likely to happen if the back door or a window is open and there is a draught
 
Honestly I can't really suggest anything because the problem could be anywhere at the moment. You say sometimes both burners work for hours and other times days, that suggests to me it's not an oil delivery problem to the cooker but doesn't necessarily mean you don't have a problem at the fuel pump. You could also have with the motor or capacitor that drives the fuel pump. It could also be a control box/box mounting plate. It really is hard to say. If you could catch a video of one of the burners losing flame and going to Lockout that would help me narrow it down a little but again it's still hard to say for sure.
 
Here is a picture of the burners
 

Attachments

  • IMG_20211017_113220.jpg
    IMG_20211017_113220.jpg
    299.4 KB · Views: 9
  • IMG_20211017_113227.jpg
    IMG_20211017_113227.jpg
    316.1 KB · Views: 10
Yes try that and be careful doing it and when the engineer returns see if he will service the burners.
Once you've broke the grout try removing the panel yourself, undo the screws ad release. If its removable you're laughing.
I really like these appliances, although I personally don't have too much experience with them, I know pressure jet burners and would be more than prepared to take my time getting to the bottom of issues. Unfortunately a lot of engineers don't like them and most who know what they're doing are close to, if not already at retirement age, so if the engineer gets you out of trouble then keep him around.
 

Attachments

  • VID_20211017_113352.mp4
    25.4 MB
Here is a copy of the report from the service. Does it look OK to you
 

Attachments

  • 16344675113526409383439521161289.jpg
    16344675113526409383439521161289.jpg
    345.1 KB · Views: 9
  • 16344675417404306225871977788931.jpg
    16344675417404306225871977788931.jpg
    321.6 KB · Views: 8
  • 16344675745538444615796782001625.jpg
    16344675745538444615796782001625.jpg
    295.2 KB · Views: 8
Ok, if it's the same fault code on both burners that indicates it is fuel related, unlikely to be both photocells, it boxes. I can hear bearings starting to play up, if so on the fuel pump that could be a problem, the pump coupling could be broken and not constantly catching, it could be the pump drive key as well. I'd also check the capacitor as well. When serviced did you notice how thorough they were in cleaning the burner out. It's possible, certainly have seen it many times but not certain the blast tubes are dirty and not reflecting the light to the cells as well. Just another thing to consider.
The report suggests the figures are ok. The boiler side has quite a high O², low CO² and subsequent high excess air, although not what one would usually aim for I'm not convinced it's enough to cause your problem and certainly wouldn't knock both burners out.
 

Reply to Rayburn 499k heating not firing in the Central Heating Forum area at PlumbersForums.net

Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock