Anthony Gray

Radiators very slow to warm up on ground floor.
I live in a two storey house with unvented hot water cylinder and closed CH system.
Boiler is on ground floor. The unvented hot water cylinder, water pump and expansion vessels are in the loft.
Ground floor CH has two port valve and radio controlled thermostat.
First Floor CH has two port valve with fixed thermostat.
The pump is working.
Both thermostats and two port valves are working.
The first floor radiators are working well and have been have been 'balanced'.
The ground floor radiators take 2 hours to warm up.
The CH pipe on the ground floor from the pump gets very hot but the CH return to the pump is just warm.
My suspicion is that the CH flow and return pipes are both connected to the same side of the pump - is this normal?
I have a photo of the pipes around the pump but don't know how to attach it.
 
Has it always been this way?, I couldn't see it working if both flow/return connected to same side.
Have you TRVs on all the ground floor rads?
Does your circ pump display the power in watts?.
what is the system (boiler) pressure?.
 

Reply to Radiators very slow to heat up in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

G
I've just bought a 3-floor house with a gas boiler on the ground floor and hot water tank on the middle floor. When I switch on the hot water at the timer panel, it works but it also heats up all the radiators above ground floor. I have to close them individually to stop this. The rads aren't...
Replies
1
Views
503
  • Question
My daughter's place has a small water leak on a ground floor radiator valve. The radiator pipework is small diameter.i.e 8 or 10 mm. A plumber is coming back in a day or so to make necessary repairs. I am a little concerned as the house has a Boilermate 2000 on the upper floor and the...
Replies
3
Views
334
I have flushed a CH system removed each Rad and removed any residue of black sludge filled the system up and treated with inhibitor. However after 2 days the water in the Overhead tank is gone red. The Ground floor rads are piping hot and the upstairs are Luke warm bleed the rads still no joy...
Replies
10
Views
649
Hi - I'm a reasonably experienced DIY plumber but just can't work out why the last new rad I've installed is cold - would really appreciate your help please. I've extended an existing 'run' of radiators - the last one on the run ( in downstairs kitchen) is cold. The first rad added is...
Replies
7
Views
620
I have just moved into a late 1990s new-build house with a small bore (about 1/2" OD pipes) gas fired boiler central heating system. All the normal radiators get hot but two of the three towel heater/radiators don't get hot and the pipes feeding them are cool to the touch even after the boiler...
Replies
4
Views
463
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock