Question about DHW temp and Legionnaires.

1 year old Combi boiler, hot and cold water is delivered throughout the flat via the main water feed
I have no water tanks or cylinder in flat just a combi boiler


Does it matter what temperature I set the DHW to? Is there a legal temperature that the hot water in your home should be set on for example my boilers DHW lowest temp is 35 degrees and the highest is 60 degrees and their is also a hot water survivor function which delivers water at 55 degrees Celsius.

I mention legionnaires as how does it occur and is there any chance of it with a combi boiler?

Any information would be appreciated many thanks
 
Legionnaires is not a problem with combi boilers, because the temperature of the water fluctuates too much for the legionella to breed.

Generally happens in storage cylinders where the constant temperature is between 35 C + 50 C.
Stored water should be kept at a minimum of 60C to kill off the bacteria
 
It's a bacteria, is probably more widespread than Covid and been around far longer, but is harmless untill there's a suitable environment for it to multiply, water @ 20c to 50c is perfect.
It then needs to be atomised small enough to enter the lungs.
 
It's a bacteria, is probably more widespread than Covid and been around far longer, but is harmless untill there's a suitable environment for it to multiply, water @ 20c to 50c is perfect.
It then needs to be atomised small enough to enter the lungs.
So water treatment does not remove kill it! So if it's this dangerous, why don't we have to boil all water coming into the home?
 
Drinking Legionella won't harm us.
Incidents in the U.K are relatively rare.
Cases originating from Domestic systems in the U.K range from almost unheard of to zero.
Although like everything else that may change in the future.

The source is either found to have come from Commercial buildings / Heathcare situations or it's never traced.
 
Not irrelevant.

The systems installed have been designed not to allow the bacteria to bloom.
The perfect temperature is 38C.
Hot water cylinders are set to 60 C to kill off the bacteria.
The bacteria remains dormant in temperatures less than 20C
Combi boilers have too much temperature variance over shorter periods of time for the bacteria to cause problems.
 
so the question raised could then be described as pointless and irrelevant in a domestic situation ?
Not irrelevant. There are laws about stored water temperature that apply to domestic.

In terms of practicality, as hot water does form vapour, it is possible to catch Legionnaries' Disease by inhaling the vapour, particularly from a shower.

The disease does need to get into the lungs, however. The issue is that the bacteria are in the mains water in low quantity and not enough to cause you to catch anything, even if, I suppose, you were to choke while drinking the water and it got into your lungs.

If the cold water is heated and stored at the right temperature, say 40°, the bacteria can breed and then the water could be dangerous. Above 55°, the bacteria stop breeding and start to be killed off slowly.

At 60°, they die off quite fast which is why 60 is the legal minimum for stored hot water.
 

Reply to Question about DHW temp and Legionnaires in the USA area at PlumbersForums.net

Similar plumbing topics

So a strange conundrum regarding water temp if anyone can help resolve, would be much appreciated. Ive tried to give as much info as possible to give a full picture but let me know if ive missed anything. I have a Baxi Avanta 25h heat only boiler. Works fine. Unvented 300ltr megaflow. Stated...
Replies
1
Views
145
Hi everyone just checking if this is right regarding water pressure and combi boiler pressure: Do hot and cold water always vary in pressure such as the following? Cold water from tap filled 1 litre jug in 2 seconds Hot water from tap filled 1 litre jug in 5 seconds Gas combi boiler pressure...
Replies
3
Views
649
Hope someone can offer some help with this issue, I have a Baxi 105e works fine no real downside, serviced looked after regularly. Have an issue with hot water, open hot water taps runs cold and indicates on boiler 60degrees or pump or pressure problem. Leave it ten seconds open taps again low...
Replies
3
Views
489
Morning everyone, Vokera gas combi boiler 35 degrees rising main 37 min to 60 max DHW temperature Top floor flat I turned my DHW dial on number 8 and took the hot water temperature from the kitchen sink and when tap was fully open it read at 51 degrees Celsius and when I reduced the tap flow...
Replies
0
Views
2K
Hi everyone, Just a query about what size in KW gas combi boiler do I need for a top floor flat (3rd floor). I have a Vokera Easi heat plus (20kW) gas combi boiler and it does the job, the radiators never go as hot as the should for example there are ten dots on the heat dial but the radiators...
Replies
16
Views
1K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock