Good morning. Just catching up on the new posts.
Also don’t forget about if there’s flow through the pump the leds will light up as the unit is acting like a generator eg there’s no power going to the pump plug
Shaun, are you saying the LED's on the pump would still work even if the pump didn't have power? When I press the speed button on the front of the pump, I can hear/feel the pump toggling through the different speeds. Also, if the pump wasn't working, surely the radiators/UFH and hot water would never warm up as there's no way the internal boiler pump could push water past the LLH and around the system!
Also S.0 refers to "no heating demand" which I would think is indicative of the boiler sensing no heat demand even with zone valve(s) open, I would have a good look at that Grundfos Pump as it may be the main cause of your problem, hopefully.
Given my comments above about the pump and the fact that I've done tests on each thermostat to force demand for each zone and can see the pump LED's turning on/off as demand is requested/removed, I'm feeling very confident the external pump is working. Whether it is connected and configured correctly is another matter!
Following this very interesting thread.
Just a few basic observations.
Pump overrun should not occur unless CH and/or HW satisfied, if boiler output still too high on max turndown then burner off but boiler circ pump and secondary pump should continue to run but overrun should not be called for. When pump overrun is called for normally, would expect secondary pump to be off. Suggest to check if pump overrun comes on with burner off with call from CH or HW.
Slow rad heat up/output not mentioned but with a LLH the boiler circ pump and external pump should be matched with boiler circ pump flowrate slightly higher?. so possibly wrong settings with boiler circ pump or more likely secondary pump or faulty pump. Also assume LLH connections correct.
So, I set the heating and hot water to start at 06:30am this morning, which is half an hour later than I usually set it, but I wanted to monitor what happened. At 07:00am the system was still heating the cylinder. The external pump was on, the system status (via the VRC 700) was showing DHW and the boiler status was S.24 (Burner ignited), so all looked to be okay, apart from that fact that the cylinder was still not to temperature (65 degrees C) after 30 minutes. There was absolutely no heat in the radiators or UFH.
10 minutes later it was showing S.20 (Warmstart demand). At 1 hour since turning on I noticed it had switched to heating demand and the radiators finally started to warm up.
I confess, I didn't see any sign of pump overrun this morning. Maybe I just didn't look at the right time (in the first 30 mins) or maybe I'm mistaken about this. However, should it really take an hour to heat up the water in a 260 litre Vaillant unistor cylinder?
Looking at the current config of the external pump. It is currently wired to rel 1 (open) and according to the chart, this suggests that d.27 determines what will happen. As this is currently set to 5, the chart says "External gas valve" for this value. I wonder if this is just incorrectly set and the engineer set d.28 to 2 when he meant to set d.27 to 2 as according to the chart, d.28 has no effect unless the pump is connected to rel 2 (open). As far as I'm aware, my system doesn't have an "External gas valve", so I'm not sure how this impacts on the pump starting/stopping.
From my observations yesterday (not this morning) it appeared that whenever the gas burner was on, the external pump was on. So, when in pump overrun mode, the gas burner wasn't on and therefore the external pump wasn't on. Again, this could be a complete red herring, but I'm trying to make sense of the current configuration and what is happening, given the fact that setting 5 for d.27 mentions "gas valve".
As the pump cable connections are inside the boiler, I don't want to take the front off to change them, so it may be better for me to simply change d.27 to value 2, rather than 5 and see what impact (if any) that has.
I appreciate the connections need to be re-done and I'll ask the engineer to look at them as he's due back soon to service the boiler.
So, although I didn't see any evidence of pump overruns this morning, I've definitely seen it happening on other days, so I'm not ruling this out completely just yet.
If it is expected to take an hour to heat the cylinder to 65 deg C then it would appear everything is working as normal and I'll just have to turn on the hot water earlier in the morning to give this time to happen, followed by time to heat up the house. However, this never used to be a problem prior to the recent upgrade, when the heating/hot water started up at 06:00 every morning and the house was toasty by the time I got out of bed at 07:00am.