I have a Vialliant ecoTEC pro 28 . last week or so it has been a bit temperamental ,sometimes comes on sometimes not .the answer was generally to add more water , my fill loop only has one tap to fill and that on;y fills a little ,i always remember two taps ,,anyway i get the usual F 75 and press reset makes the usual noise and starts up , last few this has not happened ,i have to open the the tap for a second or two and hear a little bit of water going in it then works as normal , pressure says 1.6 , this does not change , after some searching i think it may be a water sensor problem , any advice would be great
 
Ideal pressure is 1.5 bar and no more. There are a variety of reasons why your boiler might loose pressure. The difference between zero and 1.5 bar on a normal domestic pressurised heating system
is about 5 litres or two large coke bottles. There is a protocol for checking this type of system
1. look for obvious signs of damp 2. Check the prv the valve that goes to outside ..they can weep
3. watch the pressure as it can go up and then drop...thats a boiler problem.
How often does it loose pressure that is crucial in id the problem. ?
centralheatking
 
Not for a few years and then i thought there was two taps,
[automerge]1575225360[/automerge]
just checked the boiler, heating been on for 3 hours or so the screen is showing 3.6 bar . i think this is far too high
 
Last edited:
Cheers Stigster , I could top the water up thats all ., no danger of me taking the cover off .
Now angus here is how to mitigate your problem. The expansion vessel that fits inside and at the back of most combi boilers will be quite expensive to to change in terms of labour and the bespoke part. My advice is after consulting with your GSR is to get a suitable capacity exp. that can be fitted eleswhere...they are really cheap...look at
BES at Electric Ave Brum and do the same job...say the boiler type is ÂŁ150 the generic one will be about ÂŁ40.00....others will comment ...centralheatking
 

Reply to pressure ecotec pro ? in the USA area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
297
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
0
Views
49
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
57
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
0
Views
44
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
221
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock