I cleaned out the magnetic filter on my Worcester boiler for the first time and the pressure has dropped from about 1.7 bar to 1 bar. What could the reason be?
 
You've cleaned the filter out whilst the boiler had been running, which is not a problem.

Sealed systems sit from 1 - 1.5 bar as per manufacturer.

When the system gets hot the pressure rises for example 1 bar to 1.7 bar.

When you have a day off, let the system cool and check the pressure then, make sure it's around the 1 - 1.5 bar mark, I personally keep it just over 1 bar as any tiny amount of excess air may vent out of an AAV and pull it below 1 bar.
 
If you fill to 1.5 bar when cold when the heating circuit heats up it will be sitting around 2 bar, uneccsssary strain on all Pipework and joints. Better to fill to 1 bar so it’s around 1.5 when hot.
 
If you fill to 1.5 bar when cold when the heating circuit heats up it will be sitting around 2 bar, uneccsssary strain on all Pipework and joints. Better to fill to 1 bar so it’s around 1.5 when hot.

I can see where your coming from but if your sealed system can't take 2 bar when hot, I'd suggest leaving a umbrella for when the diaphragm eventually perishes inside the expansion vessel
 
I can see where your coming from but if your sealed system can't take 2 bar when hot, I'd suggest leaving a umbrella for when the diaphragm eventually perishes inside the expansion vessel[/QUOTL

Lool I’m not saying the system couldnt handle it , I’m saying why put excess pressure in the system when it’s not needed ?

Also like i said if you pressure to 1.5 bar and it gets to 2 bar when hot and over the year between services if the pressure in the expansion tank was to drop it will raise above two bar. Many engineers don’t check the level of pressure in the expansion tank when servicing.
 
The expansion vessel pre pressure is a very important setting as well, some are set at 1 bar and if the filling pressure is then 1.5 bar there will be a few litres of water reserve in the vessel while cold to make up any air venting and tiny leaks over time without the need for constant topping up, the pressure will then have to fall from 1.5 to 1.0 bar before this reserve is exhausted. If filling pressure is set to the same value as the pre pressure then this is not possible.
In general, I would suggest that the filling pressure should be 0.3/0.5 bar higher than the pre pressure.
 
1.5 bar from cold , why ???????? When any boiler works on 1 .
1.5 bar from cold , why ???????? When any boiler works on 1 .

If you look at the dials it's not just green on 1 bar it has a range 1 to 1.5

I keep saying *between*

Yes any sealed system will work at bar, but as I said IMHO I go just over 1 bar because if you've drained it down to carry out work and refill system your not always going to get all the air out so when the aav opens to let out any excess air and its just one 1 bar there's a chance the pressure could drop under 1 bar and the boiler stops working because low pressure.

I'm guessing you've always filled to 1 bar and never had a problem, as I said we have our own way of doing things
 
Have seen pre (charge) pressures of 0.5 to 1.0 bar on externally mounted E.vessels, 0.5 bar should be the very minimum where the E.vessel (and boiler) is mounted on the ground floor as any lower setting than this will result in upstairs rads circulation eventually ceasing when the water reserve is used up.
Have attached a few numbers here showing the effect of three different pre charge pressures, all with +0.5 bar filling pressure.
 

Attachments

  • Expansion Vessel Calculation Extract Rev1.zip
    10.2 KB · Views: 17
0.8 normally do mine too
 

Reply to Pressure drop after cleaning filter in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all Noticed bad smell in my drain out side put my hand down and it unclogged it for now however I checked my sewer drain and after flushing my toilet a good few times nothing is going to the sewer so don't know is there a blockage or what way it works many thanks and advice would be grateful
Replies
3
Views
424
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new brackets, dismantle that existing one and start again or I could try and re attach via those screws, removing the broken ones from the plate and wall...
Replies
0
Views
109
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
255
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
5
Views
131
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
206
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock