Discuss Pressure below 1 bar in morning when water heating comes on in the Central Heating Forum area at PlumbersForums.net

Alan stewart

Messages
4
Got baxi 800 5 months ago with new water tank and expansion vessal which is opposite water tank.
After heating off all night and water heating comes on pressure too low below one bar makes noise.
If put central heating on pressure goes over one and is OK. Pressure stays under 2. Have recently had boiler guy round as was leak on expansion vessal which has replaced. But still have the above issue.
 

Alan stewart

Messages
4
Have you topped the system up to 1.2 bar ?
Hi thank for your response, I did top pressure to approx 1.2 hoping that would help when system cold and hopefully pressure OK when hot water set to come on in morning. When comes on is just below 1 bar still happened this morning so put central heating on and was OK stopped short of 2 bar
 

Alan stewart

Messages
4
Hi thank for your response, I did top pressure to approx 1.2 hoping that would help when system cold and hopefully pressure OK when hot water set to come on in morning. When comes on is just below 1 bar still happened this morning so put central heating on and was OK stopped short of 2 bar
Wondering if it's valves as only thing not recently replaced as had pump water tank boiler and expansion vessal new
 

cjg

Plumber
Messages
475
it will be a neg pump. ie, drops a little when on, water heats up, presure will rise, leave it as it is and wait to see what happens
 

Alan stewart

Messages
4
it will be a neg pump. ie, drops a little when on, water heats up, presure will rise, leave it as it is and wait to see what happens
OK thanks, only thing is if you leave it it makes a fairly loud noise and can leave it for a few minutes and still makes noise, pressure low until putting central heating on then pressure goes up.
 

ShaunCorbs

Staff member
S. Mod
Plumber
Gas Engineer
Messages
29,465
Solutions
1
Trying running the pressure at 1.5 bar cold and set when the pump isn’t on
 

Reply to Pressure below 1 bar in morning when water heating comes on in the Central Heating Forum area at PlumbersForums.net

Similar threads

S
The boiler safety controls mean it should be safe but running the burner is only going to exasperate the problem.
Replies
8
Views
536
SJB060685
SJB060685
T
I think I’d be suspecting the pressure sensor too. If it’s losing pressure whilst the boiler is isolated it’s obviously at the boiler.
Replies
4
Views
647
Undertrained
U
N
It won't be your expansion vessel, more than likely the PRV (pressure reducing valve) is passing, these should be "drop tight" can you take a few...
Replies
3
Views
589
John.g
J
F
aha that makes sense, maybe before it was half failing (unable to fully switch over to itself) but when I set it to manual it had enough power to...
Replies
2
Views
113
fromage
F
M
And bg would have to order parts normally the Worcester lads have everything on the van
Replies
6
Views
1K
ShaunCorbs
ShaunCorbs