cant find the spec I need to service this boiler and I'm not planning in making two visits so getting info and parts ready but can't find any info on the nozzel size.Any advice would be appreciate.
 
cant find the spec I need to service this boiler and I'm not planning in making two visits so getting info and parts ready but can't find any info on the nozzel size.Any advice would be appreciate.

This may Help... Ive got more or less all Oil Boiler Manuals Handy. . .
 

Attachments

  • Potterton-Statesman 45-50L.pdf
    2 MB · Views: 22
  • PDF file.pdf
    1.5 MB · Views: 19
If you have OFTEC books or even their pocket guide it will show you how to calculate a suitable nozzle size and pressure depending on burner output needs. I did look online quickly but couldnt see the nozzle sizes etc in a manual.
 
Bare in mind a slightly bigger nozzle will require less pressure and a slightly smaller one will require more. Neither Tea-Break or I are wrong, we’ve just worked it out slightly differently, however too low a pressure and the fuel won’t atomise properly
 
The RDB1 manual says 10bar Page 8 Table A for Kerosene.

https://www.rielloburners.co.uk/images/content/downloads/RDB1-2_2902489-18.pdf

And this should give you the nozzle needed: http://www.delavaninc.com/pdf/total_look.pdf
I think this relates to the generic pump pressure range.
The boiler in question is quite small 45/50.
Therefore the correct nozzle should be .45-.50.
As SJB correctly states, going below 100PSI is not recommended.
To return to the the original post. Without wishing to be condescending, this is all bread ‘n butter stuff for any oil engineer.
 
It's categoric at a maximum of 10bar, how many times do we see posts that say follow the manufacturers instructions, concerning pump pressure and nozzle size.

The Delavan catalogue on page 7 also says to find the correct nozzle:

GPH = BTU Input / 140,000 or GPH = BTU Output/(Efficiency %) x 140,000
 
Last edited:
Ten bar is really too high and is a max limit for oil pumps on kerosine I believe. Higher can damage the pump
7 to 9 bar is range.
Diesel can be higher.

On outputs you will find the nozzle size will closely match x 1000 the btus with kerosine.
(.75 nozzle at 7 or 8 bar kerosine usually going to give 75,000 btus or more)
 
If you read burner manuals especially Riello it clearly states that it’s 10 bar max for kerosene, for the very reasons Best has mentioned above, class D is usually higher pressure and different nozzles/patterns. I didn’t feel the need to mention this before as anyone working with these burners should know this and study all sorts of manuals. As best said usual range is between 7-9 bar, but like I said too low and you’ll get atomisation and combustion problems.
If you haven’t got one already Inverness phone OFTEC and buy their pocket guide, if I remember correctly it’s about £5 plus delivery. It has these calculations in there plus all the other important information for checking tanks etc etc.
 
That's what I said 10bar maximum, the OP posted they did not have the manual for the unit, so I posted what I thought was a helpful link to the burner and nozzle calculations, the criticism's where unnecessary, be helpful by all means, but don't denigrate others for trying to help.
 
To obtain 0.75 from 75,000 you would need to divide by 100,000.

Lol! True! I did post that at 2.40 am. :)
Although tbh I just always have in my head to add 3 zeros to the smaller nozzles size (without thinking of the position of the point)
But as you say, multiply by 100,000.

Just was something I always noticed with boilers on kerosine and still applies as a rough guide despite the increase in efficiency in HE boilers.
 
Best you say multiply smaller nozzle size by 100000 to get btu’s. At what pressure is this assuming? And I assume this figure is burner input, not boiler output or efficiency must be taken into consideration?
 
Best you say multiply smaller nozzle size by 100000 to get btu’s. At what pressure is this assuming? And I assume this figure is burner input, not boiler output or efficiency must be taken into consideration?

Only saying that as a very rough estimate of boiler output for kerosine and at 7 bar or 8 max oil pressure.
At 9 bar the output will be higher.
Just really judging that on all boiler specs, of various types.
Nothing to rely on, but just an indication that a nozzle on a boiler you go to is wrong size.
 
Yeah I just done some examples on my EOGB calculator and what you say is a vary rough figure, depending on pressure and efficiency. I’ll stick to what I know lol
 
Of course its correct, It's an international standard for all manufacturers that they quote the output of their nozzles in GPH at 100psi I should think that everyone on this thread knows that.
 
Of course its correct, It's an international standard for all manufacturers that they quote the output of their nozzles in GPH at 100psi I should think that everyone on this thread knows that.

US gallons per hour at 100 psi, which always seem weird to me, but that’s how it is
 
Our UK gallons is roughly .84 of a US gallon if I’m not mistaken, but yes Best it relates to US measurement as I believe the pressure jet burner is originally an American invention
 
Our UK gallons is roughly .84 of a US gallon if I’m not mistaken, but yes Best it relates to US measurement as I believe the pressure jet burner is originally an American invention

I also tend to think on oil output of a US gph nozzle approx same in our UK gph if oil pump is set at 8 bar.
US gph is at 100psi, so at 8 bar it is 120psi which is close to converting the US gallons output to our gallons.
So say a 1.0 nozzle at 100 psi will give .84 UK gph, but multiply by 1.2 (to raise to 8bar) will give approx 1.0 UK gph.
If that makes sense. :)
 
Last edited:
The first pressure jets where used to propel vehicles and where invented by the Russian N Teleshov in 1864, adapted by a Swedish inventor Martin Wiburg and eventually became the pressure jet burner.
 
The first pressure jets where used to propel vehicles and where invented by the Russian N Teleshov in 1864, adapted by a Swedish inventor Martin Wiburg and eventually became the pressure jet burner.

Wow! Where did you find all that from?
 
A little confused there I think, a 1.0 nozzle at 100psi will give 1US gph or 0.84UK gph, got your UK and US mixed up, easy done, but as you say raise the pressure to 8bar (116psi) and it will give approximately 1UK gph.
 
Last edited:

Reply to Potterton statesman 45/50 nozzel size? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have bought an old house in rural France and it has an oil tank and Unical oil powered boiler (Italian I think). Its a beast of a thing but can't find any model info or any plates on it. I want to change the switch and thermostat to a digital wireless thermostat but I'm not sure what I can...
Replies
6
Views
581
Dear All New member here, coming looking for help. A few weeks ago I had work carried out by a British Gas Homecare service technician. It required a drain and refill of the system, and as he left, he advised my I would need to bleed all the radiators, at some point, given a few days, when...
Replies
14
Views
926
Ive got a new replacement boiler to install and the Energy Saving Trust whole house boiler sizing is no longer being allowed to be used to correctly size new boilers. Apparently there is an app you can use for room by room calculation anyone with a link. I've looked online and keep just...
Replies
0
Views
671
Hi I have been ringing round trying to have someone call out but it appears all heating engineers are booked up until after xmas so trying to find a solution if possible, any advice is much appreciated. We have an external Calor 1000litre gas tank in the garden and a Potterton boiler, we let...
Replies
0
Views
471
Hi I seek some advice on replacing an existing regular boiler. I currently have an old Potterton 10-16 Netaheat electronic, which is around 35 years old and still working OK. It is fitted to a std 'Y' plan system with boiler in utility room and separate hot water tank, pump, valve etc in...
Replies
7
Views
640
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock