Hi I'm tying / hoping to run a drain for an Unvented indirect cylinder

I need to run it now as I want to close in the building ( its in a loft conversion )

I'm having great difficulty getting someone to fit the whole system

for me , it was being done by a guy but now he can not do it as hes moved away

I'm trying obtain new quotes ( everyone's busy )

Ive been told this so far

run it in 40 mm pipe and bring it up where the cylinder is

found a sketch online is this what I need / current regs ?

also is it polypropylene pipe

The run is 3.5 Mtrs straight then drops down through soffit elbows left ( swept bend ? ) into soil pipe 700 mm

1620564503672.png
 
Thought you found a new guy to do the install ?

but it needs to be 11/2 push fit with swept elbows and clips every 450mm
 
Thought you found a new guy to do the install ?

but it needs to be 11/2 push fit with swept elbows and clips every 450mm
I have had a guy round to quote but was a little bit bolshy and said just put a 40 mm pipe into the where the cylinder is and wouldn't elaborate , I thought there would be a little more

about the discharge pipe if I put a diagram would you have a peak ? as Im not sure I understand your reply
 
Yes post one up
 
Yes post one up
Hi Shaun I've not done a diagram yet but have been doing a lot of reading ( dangerous I know ) but this is what I've gathered from yourself and others does this sound ok

The discharge pipe D2 from the self sealing waterless valve ( as shown in the diagram above )
then a swept 90 bend
a 3.3 Mtr run clipped at 450 center's
two 45 bends to achieve a drop down through the soffit to vertical
a 250 mm verticle drop
another 90 swept bend
then 600 mm into the stack

this would all be in 40 mm black or white pushfit fittings in propropylene pipe
then only thing ive found that this would not work as the pipe work goes outside and ive read
propropylene .,s not suitable oustside as its not UV resistant

other than that I've read it could be done in 22 mm copper copper but then I cant find a suitable boss connector adapter any ideas
 
Tbh it doesn’t harm it that much the uv rays there loads of push fit used externally as most of the diy places sell it

would need to be in 28mm copper due to distance
 
but in essence what I've described is ok regarding the description of the run im doing is ok in 40 mm pushfit ?

on the copper side of things the total run is 5 mtrs max ( probably less ) and thats not suitable for 22 mm ?
 
40mm is fine

Correct 28mm is required just as each elbow adds 1 m total for 22mm max is 9m so if you have 4 elbows your over
 
ah ok so if i go up too 28 mm copper could i use one of these to connect into the soil pipe
https://www.NoLinkingToThis/p/pegler-brass-compression-flanged-tank-connector-28mm/1963g

it could go into the outlet on the bossed access ive got already

hmm just thought it would need to be curved to fit contour of pipe
 
No that’s for a tank also the g3 engineer needs to do the work
 

Reply to Pipework type / design for Unvented Cylinder ( 170 L Megaflo Eco ) in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
5
Views
144
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
5
Views
139
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
176
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
256
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock