N

Nicmac

I have a ideal logic max boiler ( installed in Nov 2021) in the garage, water tank and pump in airing cupboard in the house. I have a frost stat in the garage set at 5c and a pipe stat on the return pipe to the boiler set at 10c. So can anyone explain why my radiators are still heating up on and off through the night. Whilst it's been very cold (-t4 or-5c temps) I thought the addition of the pipe stat would prevent this?
 
Because the return temp will need to get above 10c so the boiler will have to sent heat around
 
Is it a s plan system..ie 2 motorised valves..and do you have a bypass valve…that is pipe after the pump connecting to the return from the cylinder…
If the programmer is off and both zone valves closed because of that, the heat is supposed to travel up the flow ,thro the bypass and back to the boiler thro the return..until such time the return rises to 10 degrees
 

Reply to Pipe stat not effective? in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
126
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
212
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
210
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
300
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock