My gas engineer is replacing 6 gas meter boxes. He has discovered when they were installed in 1980 they used PE pipe from behind boxes. This is fine as it's underground. But, there is a metal compression joint, joining copper from box to PE pipe, which is also under ground and hence rusted.
He has advised this does not comply and needs changing. His solution was to use Philmac PE gas fittings. However, he has now advised Philmac literature advises compliant with ISO10838, which was withdrawn in 2015, and replaced with ISO17885.
Philmac are not answering calls or emails to confirm if they are compliant with new standard.
So his suggestion is either leave new connections accessible so we can use metal, or get specialist to fusion weld.
I don't fancy either of the new options, the Philmac solution is much better, but he won't progress with this until there is confirmation the fittings comply with latest standard.

Any suggestions?

Gas engineer has also posted same question elsewhere.
 
Any pictures of the set up ?
 
That looks like the supplier side eg the mains into the meters ?
 
They look like George fisher fittings


Which is what most transports use underground
 
I would replace due to the look of them and test then wrap in denso all must be done via a gas safe engineer eg no diy
 
I would replace due to the look of them and test then wrap in denso all must be done via a Registered Gas Engineer eg no diy
I agree with everything you say.
my concern is gas engineer is looking for iso17885, looks like these fitting are iso17875-2.
this means nothing to me, he’s gonna want to be able to reference this in his book. Where will he find confirmation he can use these fittings?
 
I agree with everything you say.
my concern is gas engineer is looking for iso17885, looks like these fitting are iso17875-2.
this means nothing to me, he’s gonna want to be able to reference this in his book. Where will he find confirmation he can use these fittings?

yes manufacturers instructions state can be used underground (you could email them and ask for this in writing)
 
yes manufacturers instructions state can be used underground (you could email them and ask for this in writing)
Thanks, looks like they have tech support in uk, I’ll give them a call on Monday. +44 24 7653 5535

thanks for your assistance.
[automerge]1603010854[/automerge]
Thanks, looks like they have tech support in uk, I’ll give them a call on Monday. +44 24 7653 5535

thanks for your assistance.
Gas engineer says no compression or mechanical joints can be concealed and must be accessible for inspection.
I’m a spark, our regulations are recommendations. You can deviate and following manufacturers instructions. Is Gas the same, where do we stand if manufacturer says it’s fine, but gas book says joints can’t be concealed?
 
Last edited:
Some manufacturers can override our gas regs
 
Some manufacturers can override our gas regs

Got a response from Gas Safe Register, I think this clears up a lot of doubt about using MI generally. GSR Engineer now happy to proceed.

In terms of hierarchy, the following documentation should be followed in order. Legislation (Gas Safety Installation and Use Regulations 1998), Manufacturers Instructions then Technical Guidance such as British Standards/Institute Gas Engineers & Managers etc.
 

Reply to Philmac gas fittings in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
297
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
224
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new brackets, dismantle that existing one and start again or I could try and re attach via those screws, removing the broken ones from the plate and wall...
Replies
1
Views
162
Copper pipes, I think its fair to say, is not what it used to be, the copper is getting thin while the cost is going up. Meanwhile, plastic Pushfit seems to be getting better and better, cost and convenience was always better, but now the quality is to, have we reached a stage where plastic will...
Replies
2
Views
226
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
199
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock