Discuss PEX-AL-PEX for hot water return (manifold system) in the USA area at PlumbersForums.net

Messages
35
(Bear with me this is my first post on here...)

We're putting in a manifold system for the H+C in the bathrooms of our new house (self-build). What are everyone's opinions on using PEX-AL-PEX pipe for our hot water return system, please? Good or bad idea? The pipe says: Tmax 95 degrees C / 10 bar / ISO 9001. There's another code, but the piece I have only has 070M, then it's cut. Do I need to check the rest of it?

It's hard to find my guidance online.
 
Any chance of a pic of the pipe ?
 
My understanding was that you couldn't use Plastic on a HW circulating return circuit and that draw offs had to be at least a meter in copper before going to plastic - however not sure on the type of pipe system you are using they may approve it.
 
Thanks both. Here are some pics. It's Pipex pipe, but their website wasn't very helpful. It seems to be used for UFH a lot, but assuming that's not an indicator as that runs at lower temperatures?
 

Attachments

  • IMG_20200214_104403~2.jpg
    IMG_20200214_104403~2.jpg
    81.2 KB · Views: 23
  • IMG_20200214_104809.jpg
    IMG_20200214_104809.jpg
    43.6 KB · Views: 22
Yep your fine for using it for secondary returns it’s classed as mlcp
 
Thanks both. Here are some pics. It's Pipex pipe, but their website wasn't very helpful. It seems to be used for UFH a lot, but assuming that's not an indicator as that runs at lower temperatures?

As the others have said, the multi layer pipe with the aluminium layer can be used for secondary return. The reason some manufacturers state their plastic pipes cannot be used as a secondary return is something like "Continuously circulating secondary return system are 'very different' to a heating circuit as the water is constantly replenished and circulated at high temperatures" or words to that effect.

I think the problem they have is that with a constantly replenished systems you are introducing fresh oxygen into the system and then circulating it at a constant high temperature.

These metal layer pipes are quite different from ordinary plastic pipe, even barrier pipe.
 
As the others have said, the multi layer pipe with the aluminium layer can be used for secondary return. The reason some manufacturers state their plastic pipes cannot be used as a secondary return is something like "Continuously circulating secondary return system are 'very different' to a heating circuit as the water is constantly replenished and circulated at high temperatures" or words to that effect.

I think the problem they have is that with a constantly replenished systems you are introducing fresh oxygen into the system and then circulating it at a constant high temperature.

These metal layer pipes are quite different from ordinary plastic pipe, even barrier pipe.
Thanks. I can see the potential limitations there. I'm going to try again to get a response from the manufacturer.
 
Thanks both. Food for thought. Will speak to my plumber (who's concerned about whether it'll work, but hasn't seen it yet) and my builder - who has used it previously but...isn't a plumber!
 
Have you checked with the manufacturer if it can be used on potable water?
we get 500m coils of a very similar pipe to that, from Wunda floor. But it’s only been certified for use on closed heating circuits. That’s not to say it won’t work or leak. It means the company hasn’t put it through the testing process, needed to make it wras approved.
if it isn't, you could invalidation your insurance, if there was a problem and a claim.
 
Have you checked with the manufacturer if it can be used on potable water?
we get 500m coils of a very similar pipe to that, from Wunda floor. But it’s only been certified for use on closed heating circuits. That’s not to say it won’t work or leak. It means the company hasn’t put it through the testing process, needed to make it wras approved.
if it isn't, you could invalidation your insurance, if there was a problem and a claim.
Thank you, that's a really good tip. At the moment, I can't get any response from the company (based in Spain - Pipex). I'm going to try calling them, but I thought email would be the best way, given the potential language barrier.
 
When I spoke to polypipe technical about this a few years ago they told me the constant temperature was caused the inner layer to fail bog big enough bits got back to the secondary pump to jam it.
We do a fair few secondary return systems use tectite metal tube with correct insert and there demountable fittings. You need there re rounding tool but you can bend it with a machine clip only once every meter what's not to like!
 
Hi All. I thought it was only polite to round this off... I opted to go copper for the hot water loop, but poly everywhere else. It was ÂŁ400 for labour and materials for the first phase. It'll probably be just a bit less for the other side of the house (two-stage build). I thought taking the risk on plastic was a false economy for a house I'll be living in for 30yrs+. I saved the money by installing all my own waste / soil pipes (above ground) and supply pipes from the manifolds, plus the cold loop. It was a piece of p*ss tbf. Really appreciate everyone's thoughts and views.
 
Hi All. I thought it was only polite to round this off... I opted to go copper for the hot water loop, but poly everywhere else. It was ÂŁ400 for labour and materials for the first phase. It'll probably be just a bit less for the other side of the house (two-stage build). I thought taking the risk on plastic was a false economy for a house I'll be living in for 30yrs+. I saved the money by installing all my own waste / soil pipes (above ground) and supply pipes from the manifolds, plus the cold loop. It was a piece of p*ss tbf. Really appreciate everyone's thoughts and views.

Any pics of your install?
 

Reply to PEX-AL-PEX for hot water return (manifold system) in the USA area at PlumbersForums.net

Similar plumbing topics

Hi all, new to this forum and looking for a bit of advice please. Have been noticing recently some odd behaviour with our hot water system. If we go away for the weekend, leave Friday afternoon and back Sunday night, the hotwater is lukewarm at best up our return Sunday evening. I then need...
Replies
13
Views
756
I have just moved into a late 1990s new-build house with a small bore (about 1/2" OD pipes) gas fired boiler central heating system. All the normal radiators get hot but two of the three towel heater/radiators don't get hot and the pipes feeding them are cool to the touch even after the boiler...
Replies
4
Views
451
Hi, I have two indirect water cylinders (Gledhill) connected to a gas boiler (Vaillant). The system is setup/programmed so that the tanks heat up twice a day for about 2 hours. When the tanks start to heat, one of them makes a loud vibrating noise, sometimes for about 15-20 mins, sometimes for...
Replies
4
Views
841
L
Hey everyone, I'll keep it short. Had our old system boiler replaced with a new Ideal system boiler set up. Then the problems began. First issue was the pump went faulty, so the pump was replaced. This then led to a new issue coming up where the central heating would work, but not the hot...
Replies
2
Views
1K
Hi all, I am currently renovating our 70s house a room at a time. It currently has single pipe central heating, heat only boiler and indirect cylinder with F&E tank. It's a noisy system and even when balanced, the last radiators take a while to get hot. I'm also getting air in from somewhere...