Hi everyone,

I’ve just assessed a top floor penthouse with what’s best described as Sod poor water pressure (1 bar standing, 0.25bar working) at 8/9 lmin... it has a conventional heat only boiler and cylinder in the utility, cold water storage and CH feed tank are about 3m higher in a stairwell to a roof terrace. There is about a 50m U shaped horizontal pipe run between the utility and storage tank / feed tank. There is an unmeasurably small amount of water flow at the float valves into these tanks at the best of times (float valves are new). Obviously caused by not enough pressure for the height of the building and a lot of restriction through the long 50m horizontal pipe run.

Another matter is that a previous engineer has been unable to refill the system following draining down to replace a zone valve, so the horizontal pipe run is more than likely air locked without an AAV in the ceiling void to vent. To top it all off all the walls and floors are beautifully tiled, some with engineered wood etc, lovely finish everywhere, ceilings included, no access hatches anywhere - you get the picture.

I’ve installed unvented cylinders a number of times and thats probably half the solution needed here, but it’s going to need a break tank and pump or combined accumulator and pump on the main... I’ve not had to find a solution to this kind of problem before, I was wondering if any other heating engineers have and what specification you would go with?

I also think the CH system needs to be switched to a sealed system, all the CH pipes are run in the ceiling and drop down, would be easier to clear air in a sealed system... or maybe a few AAVs in the ceiling void would be ok with the open vent boiler... what do other heating engineers think?

thanks, Lee.
 
Re: Heating System.
Pressurize it. I would never put AAV's in a ceiling space.
We do heaps of overhead heating systems and I haven't put any vents in these systems for years.
If a panel doesn't perform as well as it should, just turn off some panels and the air will eventually push itself into the radiator.
May only have to do that once a year, if that
 
Could you fit an accumulator with pump At low level in the flat?
Yes Scott_d I have considered an accumulator but the ones I’ve seen need 1.5bar min static pressure, we only have 1bar here... I’ve had a quick look at Stuart Turner Mainsboost Flomate, combined accumulator and pump, but these have a limited run time from the vessel, then switches to pump which can only deliver the same flow rate as at the inlet, although at a higher pressure which gives the effect of a higher flow rate, as I understand it anyway. Maybe someone out there who has fitted one can elaborate on this? Having said that, the 80litre version can apparently deliver 16lmin flow for 12 mins (whilst pump is idle) which is equal to 192 litres... putting it that way it sounds pretty good.

If the ST Mainsboost Flomate supplied an unvented cylinder, charging the static pressure up to 3 bar, the expansion vessel on the cylinder would then adequately boost the hot water flow (as normal) when a hot tap is opened... would this then mean the SP Mainsboost Flomates vessel would retain its pressure for longer when a hot tap is opened? Therefore benefiting the balanced cold take off with more litres per min... so blended mixer outlets could give 16+ lmin?

Alternatively I’m thinking either a Stuart Turner Mainsboost iBoost or Grundfos Home Booster (both are breaktank + pump booster sets), feeding the unvented cylinder and balanced cold take off. Customer will have to sacrifice some space in the utility. Another problem is I would have to run a new drinking water cold to the kitchen before the break tank. All finished surfaces this property so not easy. I think the SP Mainsboost Flomate can feed drinking water as there is no need for a breaktank.
 
Dab easy system would be my choice
 
Re: Heating System.
Pressurize it. I would never put AAV's in a ceiling space.
We do heaps of overhead heating systems and I haven't put any vents in these systems for years.
If a panel doesn't perform as well as it should, just turn off some panels and the air will eventually push itself into the radiator.
May only have to do that once a year, if that
The customers already had couple of engineers in who haven’t been able to clear the air... Ideal heat only boiler locks out on lack of water and you can hear there’s loads of air in the high level pipes. At the moment the system doesn’t work at all due to air locks. Maybe locking down all rads but one, in rotation until all air finds it way into the rads would work. I’ve only been to property to meet customer, just agreeing works / price at this stage.
[automerge]1590866811[/automerge]
Dab easy system would be my choice
Thanks Shaun, I‘ve heard of DAB... needs a separate break tank right? Why would you choose DAB?

What would you install if you wanted to avoid having to run an awkward cold main to the kitchen / drinking water? Do you know of a mains booster that can be used for drinking water, works on 1 bar static pressure and can increase flow to an unvented cylinder as well and all the cold taps?
 
Last edited:
All one unit


No mains boost will run an unvented I’m guessing the mains comes in under the sink unit ?
 
All one unit


No mains boost will run an unvented I’m guessing the mains comes in under the sink unit ?
That’s looks like a good bit of kit.

The main comes in in the utility room, which is also where the old vented cylinder. The main then disappears beneath finished tiled / engineered walls and floors Etc and distributes out to kitchen, 2 bathrooms and a roof terrace. I was thinking cut into main and extend it so it only goes to the break tank or booster, then connect the pumped cold to a new unvented cylinder, with the balanced cold take off connected back to the existing cold pipe that disappears in the wall to all cold taps. The unvented will also then be fed off the pumped cold.

I don’t want to have to run a new cold from the utility to kitchen for drinking if at all possible. It’s a long awkward route. I see the DAB Esybox / Esytank says suitable for drinking water, so maybe this would be a solution. I’ll give them a call Monday. Thanks for you help on this Shaun.
 
That’s looks like a good bit of kit.

The main comes in in the utility room, which is also where the old vented cylinder. The main then disappears beneath finished tiled / engineered walls and floors Etc and distributes out to kitchen, 2 bathrooms and a roof terrace. I was thinking cut into main and extend it so it only goes to the break tank or booster, then connect the pumped cold to a new unvented cylinder, with the balanced cold take off connected back to the existing cold pipe that disappears in the wall to all cold taps. The unvented will also then be fed off the pumped cold.

I don’t want to have to run a new cold from the utility to kitchen for drinking if at all possible. It’s a long awkward route. I see the DAB Esybox / Esytank says suitable for drinking water, so maybe this would be a solution. I’ll give them a call Monday. Thanks for you help on this Shaun.

yes it’s fine for potable water as it’s designed for whole house boosting
 

Reply to Penthouse flat, worst cold / hot water performance I’ve seen. in the USA area at PlumbersForums.net

Similar plumbing topics

I have a 2 pump hot water tank (Flomax 180L fitted in '94) in airing cupboard system with an Ideal classic boiler (downstairs next to an external wall) which for the most part seems to provide excellent hot water. The central heating also works fine - though sometimes I think the radiuators...
Replies
12
Views
662
I recently installed new hot and cold feeds to a new downstairs cloakroom. After refilling the system the hot taps were all dribbling, spluttering and showing signs of an air lock. I attached cold mains to a hot tap and left it running for 15 minutes, while opening up each hot tap. They all...
Replies
2
Views
496
I had my indirect hot water cylinder removed a few days ago and the central heating boiler and pump is turned off at the fuse spur right next to the boiler. I have been without hot water for a few days which is fine - The plumber left the flow / return to the cylinder uncapped as well as the...
Replies
3
Views
959
Hi, I'm new to the forum and just some background on myself. I have 4 years experience as a plumber but haven't worked in the trade in 15 years. I would say my overall knowledge is not great as I did most of the 4 years working on rinse and repeat estates of houses. I was also quite young and...
Replies
13
Views
563
R
I just had installed a Navien NPE-2 with built in recirculator pump. I have a dedicated return line. The check valve for the recirc is built into the unit; a spring check valve was placed on the cold line (per the manual) after which there is an expansion tank (on the cold line) in a T junction...