Discuss outside oil boiler fitted not correctly what to do next in the DIY Plumbing Forum area at PlumbersForums.net

D

diane herdman

we had a grant condensing boiler fitted last year, the lad works for a heating company and said would fit it. when he did he put the pipes all through the flue hole of the last inside boiler we had copper pipes all laid on top of each other. there was an electrical cable running through a copper pipe and hot and cold water pipes laid on top of each other. i realised this shouldnt be right so contacted a plumbing friend of ours which went mad, he said it was dangerous, lazy not acceptable and the pipes should have thier own bore hole, insulated and the electrical one should be put into a plastic pipe. so the lad came back sorted the pipes as advised and was meant to fit the condensing pipe and the soakaway also the plate for the hole (where flue could be changed round) as he had lost it. we went on holiday and this was meant to have been done came back nothing been done, we never hardly heard anything i kept asking about when it would be done and kept getting fobbed off. i felt you have had our money and not interested anymore. then we have recently found out that he has not had an electrician to sign off the electrical cables and has signed that he has done it to requirements, the boiler is not earth bonded, he has not put the micro filter and stop switch on for the manufacturer's recommendations for installation, the soakaway was not done neither was the condense pipe and didnt register the boiler for warranty where do we go from here
 
That’s normal for 4 pipes to be done through 1 hole normally a piece of 4” soil and insulated what does the boiler manufacturers instructions say on pipework ?
 
Piece of 4" soil pipe, 4 insulated pipes through it and a piece of overflow pipe to run cables through.

Need to see a few pictures.
 
As above
The Grant instructions tell you to use a 'spare' flue hole and a section of 110mm soil pipe for pipework.
If the boiler really is not registered with Grant try to get a Grant G1 installer to sort it out then commission.
If its a vortex pro as from 1st of this month 10 year warranty If commission by a G1 registered installer.
 
Last edited:

Reply to outside oil boiler fitted not correctly what to do next in the DIY Plumbing Forum area at PlumbersForums.net

Similar plumbing topics

Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
172
Copper pipes, I think its fair to say, is not what it used to be, the copper is getting thin while the cost is going up. Meanwhile, plastic Pushfit seems to be getting better and better, cost and convenience was always better, but now the quality is to, have we reached a stage where plastic will...
Replies
2
Views
177
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
255
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock