New install in a member of my familys house by a 'Friend?' baxi combi. .
The condense has been left running into a bucket on the side until after crimbo.
The blow off has not been done at all so would empty onto the kitchen worktop .
And most important. The vertical flue termination should be 1m from an openable window but is only 270mm from the bathroom opener. The fitter told the home owner that they should not open there bathroom window until they return to lengthen the flue to above the eaves .
None of the benchmark has been filled out and it will be like this for 2 to 3 weeks .
The company are gas safe but I couldnt find the particular fitter who came to this property on there list of engineers on gs website .are these usually up to date ?
Many thanks