Hi,

I have an oil-fired Aga with a BM oil control valve and a Flexitemp thermostatic control (see the image in this thread for an example).

When I bought the house I was told by the previous owner that the thermostat didn’t work and so he (and now I) have always run it by setting the flexitemp to the override setting which lifts the arm of the thermostat right up and allows the metering stem to rise - ie the aga runs on a high flame constantly. I assume that the high flow rate is lower than usual as the aga runs slightly cool and uses much less oil than the average oil aga. However it also that there is no way to increase the oil flow when there’s more demand on the aga.

As I was servicing it today, I wanted to get to the bottom of it. The float control itself seems to be working properly. I haven’t the equipment to measure the flow rate precisely, but the high and low flames both look to be about right.

However, when I turn the thermostat on at the socket and flip the switch from override to automatic, the aga will only ever run at a low flame - i.e. the arm on the flexitemp comes down onto the metering stem, restricting the oil flow, even if the aga is well below temperature.

I’m not an electrician so haven’t been able to test the circuit, but with the electricity switched on then the flexitemp box warms up, so it is clearly getting power.

All I can think of is that a) the arm itself needs adjusting, b) there is an electrical fault, c) there is a mechanical fault inside the flexitemp or d) the thermostat itself has failed somehow.

Does anyone have any experience with this sort of thing and could advise?

Thanks.
 
Hi,

I have an oil-fired Aga with a BM oil control valve and a Flexitemp thermostatic control (see the image in this thread for an example).

When I bought the house I was told by the previous owner that the thermostat didn’t work and so he (and now I) have always run it by setting the flexitemp to the override setting which lifts the arm of the thermostat right up and allows the metering stem to rise - ie the aga runs on a high flame constantly. I assume that the high flow rate is lower than usual as the aga runs slightly cool and uses much less oil than the average oil aga. However it also that there is no way to increase the oil flow when there’s more demand on the aga.

As I was servicing it today, I wanted to get to the bottom of it. The float control itself seems to be working properly. I haven’t the equipment to measure the flow rate precisely, but the high and low flames both look to be about right.

However, when I turn the thermostat on at the socket and flip the switch from override to automatic, the aga will only ever run at a low flame - i.e. the arm on the flexitemp comes down onto the metering stem, restricting the oil flow, even if the aga is well below temperature.

I’m not an electrician so haven’t been able to test the circuit, but with the electricity switched on then the flexitemp box warms up, so it is clearly getting power.

All I can think of is that a) the arm itself needs adjusting, b) there is an electrical fault, c) there is a mechanical fault inside the flexitemp or d) the thermostat itself has failed somehow.

Does anyone have any experience with this sort of thing and could advise?

Thanks.
Just to add some additional information:

It now seems to me that the thermostat may be basically functioning, but the arm possibly isn’t lifting quite clear enough of the metering stem.

With the thermostat on and in automatic mode, the fire in the aga is not as small as a low fire, but is visibly smaller than the full high fire that you get when in low fire mode (thermostat switched off and set to automatic). To be clear: in low fire mode there is no corona of blue flame above the burner, in high fire mode there is a large corona, and in this case there is a small corona.

The net result is that the aga is held at a low temperature.

When in manual high fire mode, the aga runs at the correct temperature (130 Celsius in the middle of the roasting oven).

I’ve considered whether the thermostat setting could be off (ie the control deactivates at too low a temperature), but the thermostat should only have two settings (low fire or high fire) so why then would I be getting a medium fire? It must be that the arm just isn’t lifting enough.

I see that the Toby controllers have a screw to adjust the arm height. Does anyone know if there is a similar adjustment on the Flexitemp controller for a BM float?
 
Just to add some additional information:

It now seems to me that the thermostat may be basically functioning, but the arm possibly isn’t lifting quite clear enough of the metering stem.

With the thermostat on and in automatic mode, the fire in the aga is not as small as a low fire, but is visibly smaller than the full high fire that you get when in low fire mode (thermostat switched off and set to automatic). To be clear: in low fire mode there is no corona of blue flame above the burner, in high fire mode there is a large corona, and in this case there is a small corona.

The net result is that the aga is held at a low temperature.

When in manual high fire mode, the aga runs at the correct temperature (130 Celsius in the middle of the roasting oven).

I’ve considered whether the thermostat setting could be off (ie the control deactivates at too low a temperature), but the thermostat should only have two settings (low fire or high fire) so why then would I be getting a medium fire? It must be that the arm just isn’t lifting enough.

I see that the Toby controllers have a screw to adjust the arm height. Does anyone know if there is a similar adjustment on the Flexitemp controller for a BM float?
Hi,

Delighted to help with all this, it is what I do for a living. You need to clean the Sliding Valve and hairline slit inside the OCV. Then test the flow rate (no special equipment needed). When the burner is working 100% on LOW and HIGH rates, you can then test to find which of the 3 components in the electric circuit have failed, and my money will be on the thermostat. All is very easy to do. Good luck - AgaDIYservice
 
Just to add some additional information:

It now seems to me that the thermostat may be basically functioning, but the arm possibly isn’t lifting quite clear enough of the metering stem.

With the thermostat on and in automatic mode, the fire in the aga is not as small as a low fire, but is visibly smaller than the full high fire that you get when in low fire mode (thermostat switched off and set to automatic). To be clear: in low fire mode there is no corona of blue flame above the burner, in high fire mode there is a large corona, and in this case there is a small corona.

The net result is that the aga is held at a low temperature.

When in manual high fire mode, the aga runs at the correct temperature (130 Celsius in the middle of the roasting oven).

I’ve considered whether the thermostat setting could be off (ie the control deactivates at too low a temperature), but the thermostat should only have two settings (low fire or high fire) so why then would I be getting a medium fire? It must be that the arm just isn’t lifting enough.

I see that the Toby controllers have a screw to adjust the arm height. Does anyone know if there is a similar adjustment on the Flexitemp controller for a BM float?
That is fab that we have an AGA specialist on here now :)

Did it work @Slonopotam ?
 

Reply to Oil-fired Aga thermostat not operating properly in the Oil and Solid Fuel Forum area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
277
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
4
Views
175
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
103
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
0
Views
39
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...