Any one had this problem oil boiler is running as normal but no flame at burner it’s a green star 18/25 external oil boiler
 
Check for 50-53 volts AC on white and black wire for motor. If that's good pull out photocell and cover and try ignition sequence again, if it starts its reading false light and it must be eliminated. If that doesn't do it the cell could be faulty, ie thinking its seeing light, test ohms with cell covered and exposed to light to see what that says. Can confirm it's the cell by removing from control box and try ignition sequence again, if it's the cell it will start and go to lockout. If it still stays in pre purge test coil resistance, should be around 100 ohms, if that's ok test for continuity on coil leads from control box. If all that's failed then I would change box but you already said it's been changed.
 
Check for 50-53 volts AC on white and black wire for motor. If that's good pull out photocell and cover and try ignition sequence again, if it starts its reading false light and it must be eliminated. If that doesn't do it the cell could be faulty, ie thinking its seeing light, test ohms with cell covered and exposed to light to see what that says. Can confirm it's the cell by removing from control box and try ignition sequence again, if it's the cell it will start and go to lockout. If it still stays in pre purge test coil resistance, should be around 100 ohms, if that's ok test for continuity on coil leads from control box. If all that's failed then I would change box but you already said it's been changed.
Yes I have changed control box and photo cell and still continues to run as everthin is okay but there is no flame at burner ?
 
Is it staying in pre purge (motor and fan running) or going to lockout after safety time? Everything I said above is is to test why it is stuck in pre purge. If it goes to lockout then it's a fuel or ignition problem, each of which can be caused by a number of problems.
 

Reply to Oil boiler not heating up in the USA area at PlumbersForums.net

Similar plumbing topics

Recently had a Viessmann Vitodens combi boiler installed, quite often when the adjacent cold mixer tap is opened the boiler starts for a few seconds! Can anyone tell me what is causing this? And how to cure?
Replies
3
Views
171
My son has an apprenticeship interview for to become a plumber and heating engineer. The have said there will be a multiple choice exam for this for suitability. The thing is my son panics during tests/exams. Is there any book I can buy him to practice the multiple choice test for the exam? What...
Replies
3
Views
348
Hi, My current hot water system needs to be replaced. Anyone got any suggestions or can recommend any plumbers around Derrimut area that won't rip me off? An office guy recommended me to apply for government rebates and get it installed through timetosave.com.au. How reliable is this...
Replies
4
Views
168
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
249
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
202
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock