Any one had this problem oil boiler is running as normal but no flame at burner it’s a green star 18/25 external oil boiler
 
Check for 50-53 volts AC on white and black wire for motor. If that's good pull out photocell and cover and try ignition sequence again, if it starts its reading false light and it must be eliminated. If that doesn't do it the cell could be faulty, ie thinking its seeing light, test ohms with cell covered and exposed to light to see what that says. Can confirm it's the cell by removing from control box and try ignition sequence again, if it's the cell it will start and go to lockout. If it still stays in pre purge test coil resistance, should be around 100 ohms, if that's ok test for continuity on coil leads from control box. If all that's failed then I would change box but you already said it's been changed.
 
Check for 50-53 volts AC on white and black wire for motor. If that's good pull out photocell and cover and try ignition sequence again, if it starts its reading false light and it must be eliminated. If that doesn't do it the cell could be faulty, ie thinking its seeing light, test ohms with cell covered and exposed to light to see what that says. Can confirm it's the cell by removing from control box and try ignition sequence again, if it's the cell it will start and go to lockout. If it still stays in pre purge test coil resistance, should be around 100 ohms, if that's ok test for continuity on coil leads from control box. If all that's failed then I would change box but you already said it's been changed.
Yes I have changed control box and photo cell and still continues to run as everthin is okay but there is no flame at burner ?
 
Is it staying in pre purge (motor and fan running) or going to lockout after safety time? Everything I said above is is to test why it is stuck in pre purge. If it goes to lockout then it's a fuel or ignition problem, each of which can be caused by a number of problems.
 

Reply to Oil boiler not heating up in the USA area at PlumbersForums.net

Similar plumbing topics

Hi. I hope some one can help. I have a condensing oil burner and it runs fine but the radiators don't heat. Heats the hot water fine. The pump runs and the thermostat turns the boiler on and off. Thinking it could be a thermistor. All help greatly appreciated.
Replies
1
Views
308
Hello want to know on how do you calculate size of expansion tank for closed heating systems . for example 500 meters of 16mm underfloor heating and 4 double ~1000mm radiators , hot water cylinder coil , and oil boiler
Replies
2
Views
478
Any advice welcome as plumber stumped Had 36-46 grant vortex utility boiler 7 years no problem recently oil tank move and tigerloop install (tank about 1m lower). 10 days later and boiler either doesn't fire or fires stops, fires runs splutters stops. Most it runs now is 10 mins, but that's...
Replies
4
Views
572
G
I have a danesmore 20/25 oil boiler and it is firing up but it’s producing no heat to the water or the radiators My next door neighbour an electrician has checked the cylinder and thermostat and they all check out ok so he thinks the problem is within the boiler Can Someone help give me some...
Replies
1
Views
381
Hi there. I have Grant oil fired boiler which when cold, takes multiple times to fire up. It will run for say 20 or 30 seconds with hot exhaust gases then it stops. The fan is still going then it starts off again and stops again. After 4 or 5 goes it runs fine. When the boiler gets up to...