Search the forum,

Discuss Ofsh Reset needed after every thermostat shut off. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Messages
8
Hi, wondering if any of you have come across a gun type oil burner that needs reset every time the thermostat shuts it off? What can cause this? I have a spare known good burner, I have swapped over control box and photo resistor but still does it. Once started burner will run happily for hours. Once zone thermostat or boiler thermostat shuts it off it won't restart on it's own without reset. It's not a proper lockout as the red light is not illuminated but still requires the button to be pressed. Any ideas?
 
It's a bentone st108, just to confuse things a bit for you it isn't running on kero. It's been converted to run on waste engine oil. So co2 and stack temps wouldn't be within spec anyway. All main functions still controlled with original control box except nozzle preheater. I did try this burner before converting it and it was doing the same thing on kero. It will run happily for hours on end as long as thermostats call for heat. Once power it cut, button needs pressed.
 
Are you controlling this through a Honeywell 834 box? The symptoms that you describe is that the burner is loosing the permanent live. It always needs to be reset when cold starting.

Suggest that you recheck the wiring configuration - make sure that the polarity is correct too - albeit normally if that is incorrect, it won’t fire at all.
 
Last edited:
The live is switched through the boiler stat, same as the old boiler was and it worked fine this way, I'll investigate this a bit further when I get home thanks
 
Last edited:
Sorry i ment it was wired the same as the old burner. Never changed the boiler. both burners are st108's. Looking at the bentone installation pdf from Google, there is no permanent live, just live, neutral, and earth, with the thermostats switching the live. Which is the way it is currently wired.
[automerge]1571854414[/automerge]
Problem found! It wasn't anything to do with the burner at all it was a solid state relay on the pid temperature controller. Brambles you were bang on, the boiler thermostat does not completly break the circuit, whereas my solid state relay after the stat did.
 
Last edited:

Reply to Ofsh Reset needed after every thermostat shut off. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Sticky
Morning to any Australians lurking around! Register its free, then message me, I'll sort your account out for you. We will need a moderator from each main country too. I'll post this in the Australian forum now.
Replies
0
Views
59
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock