Old setup.
Vented system - indirect
x2 Cold water tank in the loft. x2 80L Hot water tanks, regular boiler and stuart turner 4bar twin shower pump for the master bedroom shower. Worked pretty good, although the tanks were manky and old. The shower though was epic and used to blast water out. The house was gutted for refurbishment so plumber advised to change the set up for a new unvented system, that would deliver mains water pressure throughout the house. which it does.

New set up
Kingspan 300L horizontal tank. No shower pump and just the regular boiler. It’s all installed correctly, signed off and actually works quite well. All the taps and showers get mains water pressure.

Problem
I got too used to the shower pump pressure. The showerhead we have is an XL rainwater shower head and used to love the water blasting out. Whilst the showers still ok, it's just ok and not amazing anymore. If the shower in the family bathroom is run, there's a slight drop in pressure which i was expecting, but this makes the shower experience even less enjoyable.

Is there a solution?
We can’t install the same shower pump on the mains as it would draw too much water from the rest of the house and stop the other taps working - and probably mess with neighbours too. Assume this would also stop things like toilets refilling and draw air once water supply is exhausted.

So my questions are..... What is the solution for me to have a dedicated water supply for the shower again, so that I can use the pump?
Can I install a smaller vented system in addition to the unvented system that I have? The plumbers going to have a think on the best way of achieving this and let me know a price, but thought I’d ask on here too.

I know it’s potentially an expensive addition... but it just depends on cost. The shower is absolutely ok as it is, but i know how good it was and just wanted to make it awesome again.

Are there any other solutions that can be used with the new unvented tank I have?
 
Is the main adequately sized to the Unvented, do you know what your water pressure? An Unvented will only be as good as your incoming supply and pipe sizes for pressure and flow rates. Do you know what pipe sizes are to your shower valve?

If all of the above are OK and correct then you could go down the route of an accumulator, however this is like the size of another Unvented cylinder so you would need the room for this.
 
accumulator
Will google this now - I think the plumber mentioned this

Is the main adequately sized to the Unvented, do you know what your water pressure? An Unvented will only be as good as your incoming supply and pipe sizes for pressure and flow rates. Do you know what pipe sizes are to your shower valve?

If all of the above are OK and correct then you could go down the route of an accumulator, however this is like the size of another Unvented cylinder so you would need the room for this.

I believe so. If i remeber correctly, I think i have 12 or 15mm pipe to the shower. And flow rate in the kitchen tap was cira 12 -14L per min. It was decent. Don't quote me on these.

I think part of the issue is that the new tank, sits in the loft space ontop of the single story extension on the side of the house. The shower pipe then runs up vertically about 1.5-2 meters to the 2nd floor loft then horizontal again before it goe to the en suite shower. (so two story house, with 1 story extension - tank and boiler is in this roof space)

I have plenty of space here or in the 2nd story loft space where the cold water tanks used to be.
 
As EvilDr has said accumulators are large, they need to be sized correctly. The give about 50% of volume boosted pressure, so a 100 litre accumulator will only give about 50 litres of boosted pressure before it drops off and needs to fill again. Because of this working principle you would need a lot of space to install the correctly sized one as he mentioned above.
 
As EvilDr has said accumulators are large, they need to be sized correctly. The give about 50% of volume boosted pressure, so a 100 litre accumulator will only give about 50 litres of boosted pressure before it drops off and needs to fill again. Because of this working principle you would need a lot of space to install the correctly sized one as he mentioned above.

Just reading online - maybe i'm misunderstanding but it says "A common misconception. Accumulators do not increase water pressure. They simply allow the system to work at its maximum pressure capability. Each hot water system has a standing pressure and a working pressure. Just as it sounds, “standing pressure” is the pressure that exists when no outlets are being used and the water is at rest. This pressure will drop to “working pressure” when taps or showers are being used. "

So if have this installed, will I be drawing hot water from the new unvented cylinder and the cold from this accumulator, all at mains pressure - and then the shower pump drawing water from both (its a twin feed pump for both hot and cold?)
 
Yes you are right. An accumulator does not increase dynamic pressure, it just maximizes it, sorry I should have worded it better. Yes they are installed on the cold mains, hot water will be drawn from the cylinder, which in turn fills and supplies from the cold main accumulator. They can be installed virtually anywhere within the property but must be sized correctly as I said. If its boosting all outlets, hot and cold then this will be a large accumulator. What did you say your incoming pressure and flow rates is to the property? As mentioned above size of pipework, both into and around the property has a big part in what you'll achieve at outlets.
 
Just reading online - maybe i'm misunderstanding but it says "A common misconception. Accumulators do not increase water pressure. They simply allow the system to work at its maximum pressure capability. Each hot water system has a standing pressure and a working pressure. Just as it sounds, “standing pressure” is the pressure that exists when no outlets are being used and the water is at rest. This pressure will drop to “working pressure” when taps or showers are being used. "

So if have this installed, will I be drawing hot water from the new unvented cylinder and the cold from this accumulator, all at mains pressure - and then the shower pump drawing water from both (its a twin feed pump for both hot and cold?)
Before considering any of that you need to check your static and dynamic water pressures, and flow rates (At a outside tap, kitchen tap and shower).

Other things to consider are whether dirt has got in the system when you've had the upgrade and whether the filters on the shower are possibly blocked...

A picture of your install might help too of the cylinder and components.
 
Before considering any of that you need to check your static and dynamic water pressures, and flow rates (At a outside tap, kitchen tap and shower).

Other things to consider are whether dirt has got in the system when you've had the upgrade and whether the filters on the shower are possibly blocked...

A picture of your install might help too of the cylinder and components.
I'll take some pics tonight and try and do some measurements too.
 
Just for your info an unvented needs a min of 3.5 bar and 20 lpm
 
Just for your info an unvented needs a min of 3.5 bar and 20 lpm
Whilst yes that's true for it's optimum operating performance an Unvented cylinder at lower pressures and lower flow rates than this will still deliver decent performance, much better than a combi boiler.

For instance our Static Pressure is 2.5bar, i've never actually got round to measure the dynamic. But at this we get 18lpm at the large showerheads, and can run two rain head showers at once without much decrease in performance - more than what we would out of a combi.

So yeah it'd be ideal to have 3.5bar and 20lpm, however I don't think it's always essential. Many places round us can't even top their boilers up to 1.5bar the pressure is that poor! - and yes I agree in that situation a Unvented is pointless.
 
Is the shower new or the same as before the work?
judging by write up same as before a rain shower head which to me as the name suggest should not be thundering out but like being under a rain shower i suspect with the pump it made it too powerful now
it probably showers as it was designed to
 
Yes you are right. An accumulator does not increase dynamic pressure, it just maximizes it, sorry I should have worded it better. Yes they are installed on the cold mains, hot water will be drawn from the cylinder, which in turn fills and supplies from the cold main accumulator. They can be installed virtually anywhere within the property but must be sized correctly as I said. If its boosting all outlets, hot and cold then this will be a large accumulator. What did you say your incoming pressure and flow rates is to the property? As mentioned above size of pipework, both into and around the property has a big part in what you'll achieve at outlets.

I'd only use it on the shower outets, the others are fine. If I used an accumulator, would I still use my shower pump too?

judging by write up same as before a rain shower head which to me as the name suggest should not be thundering out but like being under a rain shower i suspect with the pump it made it too powerful now
it probably showers as it was designed to

It never thundered out as such, but it was good hard pressure. Now its just like a nomal tap and mediocure flow.
 
Now that you're on mains pressure hot water I thought you wouldn't use a shower pump?

as I mentioned at , pressure is fine on all taps and outlets, it's just slightly dissapointing on the shower. I meant its still decent but its not as forceful as it used to be with the previous pump, which is why i'm trying to find out how I can restore this level of pressure from the shower, as a pump cant be installed onto the incoming mains.

Ideally, all i want is my hot and cold on the shower only pumped/high pressure - everything else is perfect. looking for the most cost effective solution as I dont want to spend an arm and leg as the new setup has already cost a fair bit.
 
Yes sorry I misread your comment, I read it as you wanted to use a shower pump again. As you said above this is a no. Pumps can be put on incoming mains but must be done properly with a breaker tank. This is used when your incoming mains is below 1.5 bar or so. You need to remember your old shower pump probably generated more pressure than what your incoming mains is, which will obviously reduce the performance of the shower.
 
Yes sorry I misread your comment, I read it as you wanted to use a shower pump again. As you said above this is a no. Pumps can be put on incoming mains but must be done properly with a breaker tank. This is used when your incoming mains is below 1.5 bar or so. You need to remember your old shower pump probably generated more pressure than what your incoming mains is, which will obviously reduce the performance of the shower.

Well I do want to use my pump again, if it can be permitted to do so, but I understands it will need its own tank to do so. watch this space.
 
Well I do want to use my pump again, if it can be permitted to do so, but I understands it will need its own tank to do so. watch this space.
To do that you'll need basically your old set up refitting just for that shower, then a way of heating a cylinder. If you're using a 4 bar pump, you'll be needing a decent size cylinder to supply this also....you're already in to a decent amount of cost to do that.

Seems madness to me. Are you not just being unrealistic about the performance of the shower? Surely if the cylinder has been fitted correctly and everything else is correct - Pipe sizing, filters clean, pressure, then you'll be getting more than a decent shower out of an Unvented HW system.
 
To do that you'll need basically your old set up refitting just for that shower, then a way of heating a cylinder. If you're using a 4 bar pump, you'll be needing a decent size cylinder to supply this also....you're already in to a decent amount of cost to do that.

Seems madness to me. Are you not just being unrealistic about the performance of the shower? Surely if the cylinder has been fitted correctly and everything else is correct - Pipe sizing, filters clean, pressure, then you'll be getting more than a decent shower out of an Unvented HW system.

I almost agree with you here. He said its perfectly normal, but its just hard when you from from an awesome shower to an OK shower. as I said, perfectly happy with the other shower and taps, it's just think one becuase of the size of the head. As i've had high expections of the shower previously in comparision, i think im just a little underwhelmed. I might post clips from the performance before and after the install.

My plumber suggested somehting similar..... I was thinking if he does it for say £2-300 i'd probably do it, as at the moment, its acceptable with no other outlets on. I've not yet tested with with say a kitchen tap and the other shower, and the washing machine on and a toilet being flashed. I imagine it would drop a fair bit! I think 100L should do it as I had 2 80L tanks before and that was fine for a few showers.
 
I almost agree with you here. He said its perfectly normal, but its just hard when you from from an awesome shower to an OK shower. as I said, perfectly happy with the other shower and taps, it's just think one becuase of the size of the head. As i've had high expections of the shower previously in comparision, i think im just a little underwhelmed. I might post clips from the performance before and after the install.

My plumber suggested somehting similar... I was thinking if he does it for say £2-300 i'd probably do it, as at the moment, its acceptable with no other outlets on. I've not yet tested with with say a kitchen tap and the other shower, and the washing machine on and a toilet being flashed. I imagine it would drop a fair bit! I think 100L should do it as I had 2 80L tanks before and that was fine for a few showers.
Have you tried changing your shower head?
 
Fit a smaller size shower head and save the planet.
Useful response :)


For others- here are pics of the set up in the loft
 

Attachments

  • B100350B-91B0-48D7-ACEC-72D7FE0DA92C.jpeg
    B100350B-91B0-48D7-ACEC-72D7FE0DA92C.jpeg
    118.6 KB · Views: 33
  • B47AE349-50FA-49DF-8CAF-51E5F25C549C.jpeg
    B47AE349-50FA-49DF-8CAF-51E5F25C549C.jpeg
    124.3 KB · Views: 35
  • 65F55B49-7B6C-4FFE-90CA-0EA45D9CEBB0.jpeg
    65F55B49-7B6C-4FFE-90CA-0EA45D9CEBB0.jpeg
    133.6 KB · Views: 35
  • 8A2D0428-F040-4C89-B323-16683C87230C.jpeg
    8A2D0428-F040-4C89-B323-16683C87230C.jpeg
    124.4 KB · Views: 36
  • AE441A57-FD1D-425F-BA8F-666B118E0601.jpeg
    AE441A57-FD1D-425F-BA8F-666B118E0601.jpeg
    92.6 KB · Views: 34
Useful response :)


For others- here are pics of the set up in the loft
Well seeming the materials to do that will cost more than £2-300 I don't think you've got any chance there.

Can you see the size of the pipe incoming to the combination valve? (The one next to the white vessel which is brass colour). With all the insulation it's difficult to see pipe sizes.

But first off, it doesn't appear they've done balanced cold supplies. Which won't help.
 
Hey
Well seeming the materials to do that will cost more than £2-300 I don't think you've got any chance there.

Can you see the size of the pipe incoming to the combination valve? (The one next to the white vessel which is brass colour). With all the insulation it's difficult to see pipe sizes.

But first off, it doesn't appear they've done balanced cold supplies. Which won't help.

I’ll have a look again or ask the plumber when i can.

How can you tell it’s not balanced on the cold supplies?
 
becasue he would have taken the balanced cold feeds fron then combination valve the rear tapping
 
Bit of an update as I've properly used both showers today simultaniously for the 1st time since the new set up was installed.

-Main shower on with nothing else on - was ok.
-2nd shower went on - pressure dropped a little as expectd- but still just about ok but little weak
-Toilet flushed and tap opened - water stopped flowing in both showers. mrs was NOT HAPPY as she was taking a shower haha.

I cant deal with that.

Spoken to the plumber in regards to a solution.
Appears that an accumulator, whilst ideal, wont work as the size of tank needed just wont be fit sensibily or logistically.

The suggestion is to re-install a pair water storage tanks back into the level 2 loft, and if i understand correctly will work in the following way:

-Both showers will be fed via the twin shower pump from cold tank level 2 and hot unvented cylinder on level 1.
-incoming mains supply will top up the cold tanks on level 2 as they empty
-hot water will be pumped from hot unvented cylinder for everywhere else using a 2nd sinlge pump that we used before (I think this is what he said but i might be wrong about that.)

How does this solution sound? He said this will effectly work as its a breaker tank. Just need to work out costs. I know it will be a bit but I dont really have a choice.

A little dissapointed tbh as I kind of wish I had just stuck with the original set up which did what it needed to do and fairly well. All the research I did and people I spoke to though suggested that the new unvented system was the way forwards..... cant help but feel like it was money wasted at the moment.

I aslo asked what the flow rate was and it was circa 13-15L per minute at the mains
 
What’s your mains pressure ?

nothing open ?

one tap open ?
 
What your plumber is suggesting is incorrect. You can't pump out of an unvented cylinder, you cannot also pump the cold from the tank and then have the hot supplied from the unvented.

He clearly doesn't know what he's doing, you need to get someone else in who can advise you much better.

As @ShaunCorbs says when need to know you incoming pressures, which you've been asked for a few times yet haven't provided them. You need to know these before you make any decision on what route to take.
 
What’s your mains pressure ?

nothing open ?

one tap open ?

I cant remeber if i'm honest and I don't have a guage. However, as i've mentioned before, pressure at the taps is perfectrly fine at the moment, when the showers are not on.
[automerge]1577373831[/automerge]
What your plumber is suggesting is incorrect. You can't pump out of an unvented cylinder, you cannot also pump the cold from the tank and then have the hot supplied from the unvented.

He clearly doesn't know what he's doing, you need to get someone else in who can advise you much better.

As @ShaunCorbs says when need to know you incoming pressures, which you've been asked for a few times yet haven't provided them. You need to know these before you make any decision on what route to take.

I will try to get these readings.

As for what he's suggesting, i've only wrote what I think he think he said - i could be wrong.
 

Reply to Not happy with with new unvented system, although it works fine. Shower pressure issue in the Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Creating content since 2001. Untold Media.

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock