Hi All, New to this forum and was hopefully looking for some advice. I have a 3 storey property on a s plan system, the boiler is floor standing mexico 29kw which is located on the ground floor, the cylinder cupboard in located on the third floor. I intend to cap off the existing 5 ground floor rads which are all on drops, the underfloor heating 7 port manifold will be fitted in the garage. Does the flow and return to the manifold T straight off the flow and return coming out of the boiler?? Please help, as it would be near on impossible to take any pipework or wiring from the cylinder cupboard to the new underfloor heating manifold.
Going to use Continental Underfloor heating materials.... any reviews on this product. Also underfloor will be a 3 zone system with 3 stats .... Thank you guys
 
You need to pick up the flow and returns to the ufh direct from the boiler flow and returns. the ufh must be allowed to fire the boiler independantly of your upstairs rads
 
As the pump is in the airing cupboard you are going to have to take your feed (with zone valve from there) And depending on your other zones your return might have to go there as well . Alternatively you are going to have to put another pump and zone from the boiler flow which will then feed the underfloor manifold and pump .
 
Last edited:
Thanks for your help, basically I have to fit a pump and zone valve from the 28mm copper flow from the boiler to the u/f heating pump and then return back to the boiler ?
 
Status
Not open for further replies.

Reply to New underfloor heating to work with existing s plan .,,,, Please Help in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
388
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
217
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
308
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock