Hi,

I recently purchased a cottage type bungalow and currently there is no central heating in the house only electric storage heaters.
I am in the process of removing all the storage heaters and installing the new central heating.
All the floors in the house are cement and all the exterior and internal walls are full of king span or glass wool insulation. Making it a real headache to get pipes to the radiators.

My plan at the moment is to run 22mm flow and return from the boiler into the loft space to 22 x 10mm manifolds and drop feed the radiators down behind the walls and then behind skirting boards and up to the Rads. Most of the Rads will be underneath windows. All runs of 10mm pipe will be +/- 5m flow and 5m return back to the manifold. The largest radiator in the house will be 1100 x 600 double, 8 x Rads in total.

I also plan to fit an indirect unvented cylinder in the loft space and pipe the coil in 15mm.
Central heating boiler is a Firebird enviromax outdoor oil boiler.

I know a lot of people don’t like to use 10mm for central heating but seems to be my only option without channelling the cement floors.

I have recently read that a lot of new build houses central heating systems are done a similar type way. Do you guys think what I have described will work OK with the length of runs of the 10mm pipe?


Thanks in Advance
 

ShaunCorbs

S. Mod
Plumber
GSR
Messages
23,256
Reaction score
6,236
Need to be qualified to fit the cylinder also 22mm is required

And 15mm to the rads I would do
 

Pickwickpick

Plumber
Messages
494
Reaction score
157
As above, for the safety of yourself, your family & your neighbours, please get someone who is G3 qualified to fit the unvented cylinder.

With regards to the piping, if I was in your position I would go for 15mm and channel the floor if need be. Seems a shame to go to all this effort only to stand an increased risk of blockages and issues further down the line that will be expensive & disruptive to fix.

Also as a general rule of thumb, anything that is common practice in new builds is almost certainly not best practice.
 
OP
S

swhyte1981

New Member
Messages
8
Reaction score
1
Appreciate the reply's.
For sure I will have qualified Plumber to fit the boiler and cylinder.
My plan to reduce cost was to rough in all the pipework and have a plumber do the final install.

Agreed 15mm would be much better than 10mm.
But do you think it is possible from what I described for the system to work OK if well maintained and plenty inhibitor?

Thanks
 
Messages
229
Reaction score
85
Do a lot of systems like that and don't have any issues. 15mm is better and preferred, but not always ideal for the install.
 

king of pipes

Plumber
GSR
Messages
3,088
Reaction score
1,186
It will work if executed properly alot of new builds are done that way the boiler and unvented cylinder are notifiable so will need fitted by a registered installer , any work you carry out yourself will need checking and pressure testing . Kop
 

ShaunCorbs

S. Mod
Plumber
GSR
Messages
23,256
Reaction score
6,236
Will have problems later as the bore is reduced to 6mm in parts like most new builds
 

Rob Foster

Well-Known Member
Messages
2,083
Reaction score
495
Appreciate the reply's.
For sure I will have qualified Plumber to fit the boiler and cylinder.
My plan to reduce cost was to rough in all the pipework and have a plumber do the final install.

Agreed 15mm would be much better than 10mm.
But do you think it is possible from what I described for the system to work OK if well maintained and plenty inhibitor?

Thanks
No matter how much you ask us Mr1981 ...you will get the same general reply ...22mm main supply and 15mm to the rads. Plus the visual effect of microbore to the rads and anywhere seen ...immediately
says old, amateur , skin flint
cheap etc. if you will want to extend or sell on your plans for
microbore are plain wrong.
centralheatking
 
OP
S

swhyte1981

New Member
Messages
8
Reaction score
1
Thanks for the feedback.
Will take onboard and may go with channeling floors for 15mm, also good to know that the 10mm systems can work.

Cheers
 

Allgoode

GSR
Messages
259
Reaction score
72
Don't forget to forget to run you 15mm Hep2o or Speedfit in conduit to protect it in the floors & then have a 90 degree fitting & bring it up in 15mm copper.

Looks a lot better than other options.

Andy
 

Rob Foster

Well-Known Member
Messages
2,083
Reaction score
495
Don't forget to forget to run you 15mm Hep2o or Speedfit in conduit to protect it in the floors & then have a 90 degree fitting & bring it up in 15mm copper.

Looks a lot better than other options.

Andy
dead right 15mm copper upstands from floor up to rad valves everytime chking
 

king of pipes

Plumber
GSR
Messages
3,088
Reaction score
1,186
15mm plastic fittings buried in the floor or walls hmmm personally I would try and avoid this , but each to their own . Kop
 

Jimmy18

GSR
Messages
35
Reaction score
11
Why not just use plastic coated copper in the floor. Denso tape all the joints, will last forever.
Make sure you make up your rads and measure from centre to centre of your valves for your first fix otherwise will look carp
 

SimonG

Plumber
Esteemed Member
Messages
18,339
Reaction score
9,864
Get your plumber on board now. Will save headache later.
 

Best

Plumber
Messages
9,860
Reaction score
3,875
Why not just use plastic coated copper in the floor. Denso tape all the joints, will last forever.
Make sure you make up your rads and measure from centre to centre of your valves for your first fix otherwise will look carp
Or better to have the rads screwed to walls first and pipe to them, if possible
 

Forum Sponsors

Corgi - Plumbing Supplies for Professional Plumbers - Plumb Advice

Plumbase - Plumbing Parts for Plumbers - Plumbers Advice

Power Shower Booster for Power Showers - Plumbing Advice

Underflor Heating Systems by uHeat - Plumbing Advice

Wetroom Supplies by Wetroom Store

Nicobond - Wetroom and Tiling Supplies - Plumbers Installation Advice

Corgi - Plumbing Supplies for Professional Plumbers - Advice for Plumbers

Do you have a DAB radio for work?

  • Yes

  • No


Results are only viewable after voting.

Latest Plumbing Advice

Top Bottom