potterto boiler 23 years old, Drayton mid point actuator.
Central Heating only works when water also on & stat works normally. When CH only, the stat shows a bright light when calling heat and dim light when at temperature.
I changed the stat and it made no difference.
The three way valve seems to work ok (slider moves from W to both to CH) but when you take the head off and use pliers to turn it is very clunky.
Pump seems to be working ok.
Any ideas?
 
potterto boiler 23 years old, Drayton mid point actuator.
Central Heating only works when water also on & stat works normally. When CH only, the stat shows a bright light when calling heat and dim light when at temperature.
I changed the stat and it made no difference.
The three way valve seems to work ok (slider moves from W to both to CH) but when you take the head off and use pliers to turn it is very clunky.
Pump seems to be working ok.
Any ideas?
I take it this used to work until recently?

Try turning the heating system off at the isolator and then on again.

If still not working:

I don't think you've proved that the actuator head is working correctly (is it making the right wires live at the right times and is it moving to the right places under motor control?)
If the valve itself is 'clunky' then either it may be preventing the actuator head from doing its job, or it may have been leaking and has caused the head to malfunction.

If you have a good logic for faultfinding and know your way around a voltmeter (not a volt stick), then you may be able to check if the actuator head is working and if it is receiving the right voltage on the right wires. This would help you pinpoint what needs replacing.

Other than that, this really is a job for a skilled plumber or heating engineer. Most electricians won't understand their way around heating controls.
 
I take it this used to work until recently?

Try turning the heating system off at the isolator and then on again.

If still not working:

I don't think you've proved that the actuator head is working correctly (is it making the right wires live at the right times and is it moving to the right places under motor control?)
If the valve itself is 'clunky' then either it may be preventing the actuator head from doing its job, or it may have been leaking and has caused the head to malfunction.

If you have a good logic for faultfinding and know your way around a voltmeter (not a volt stick), then you may be able to check if the actuator head is working and if it is receiving the right voltage on the right wires. This would help you pinpoint what needs replacing.

Other than that, this really is a job for a skilled plumber or heating engineer. Most electricians won't understand their way around heating controls.
Thanks for reply. Will try tonight. Have added a video to show the clunks.....is this normal. Mike
[automerge]1575474709[/automerge]
Thanks for reply. Will try tonight. Have added a video to show the clunks...is this normal. Mike
Actuator moves to right place at the right time.
 

Attachments

  • IMG_8401.MOV
    16.4 MB
If the Boiler works for Hot water you can more than likely rule that out.
The chances are it is going to be the programmer, room stat, Motorised valve, wiring etc.
All the component parts can be tested so there is no need to guess and that method will only cost money unnecessarily.
How competent are you with electrical work?
 
If the Boiler works for Hot water you can rule that out.
The chances are it is Either the programmer, room stat, or Motorised valve.
All the component parts can be tested so there is no need to guess and that method will only cost money unnecessarily.
How competent are you with electrical work?
I am confident to check voltage etc but lack some proficiency and which wires to check. I may have an old programmer so will try that out. I am trying to get hold of a plumber that helped me 6 months ago with a blockage. Thanks for help. Is the noisy valve normal?
 
I'd be suspicious of the valve head. But this needs to be tested on certain coloured wires. This really is a job for someone with a good understanding of electrics. I'm sure if you feel confident then someone will guide you through it but ONLY if you're confident
 
Thanks for help. Put an old programmer in and problem persists. Checked wiring of mechanical valve (Actuator) and all secure. So down to actuator or 3 way valve or perhaps pump but that works when water/CH on together.
 
I'm a bit concerned how you've tried a new stat and programmer. Are you sure you're connecting the right wires to the right place, you could be further complicating things. Really it needs to be tested from programmer to stat and to valve to see what voltage is where. Like I said earlier from what you've described I suspect it is the valve body or head.
 
Thanks. The programmer is a clip on to a base which holds the wires. Two minute clip on so no wires and stat was 4 simple wires. The valve was clunky when moved with pliers so not sure if that is normal. I changed the actuator about 5 years ago and quite proficient at replacing bits.
Is a clunky valve normal??
 
The spindle could be sticking and preventing the valve from opening fully. The valve has switches inside that depending on what's called for depends what's live and isn't. With everything off and then turn CH only on I would be looking for a feed from programmer, through stat and then to valve, ultimately testing for feed on the orange wire. HW off must be energised as well.
 
A blockage could cause that yes. You would benefit from a power flush if the system is riddled with black iron oxide (sludge). This is something you should have mentioned in original post, would of saved a whole load of trouble lol
 
I suspect the clunk in the video is due to the fact that the pump is running as you move the valve? If so, the pressure surge caused by the resistance to flow as you close off the waterway with less resistance may be resulting in a clunk, possibly as the pressure slams the internal thing against the valve seat? That's my hunch anyway. Let me know if this proves to be right.
 
As I tested programmer using an old one I am going to flush system and change the 3 way valve. I can turn spindle in new one by hand. The old one needs pliers. Probably full of hunk. Hopefully flushing a couple of times leaving water on will help. Once that is done will attach the existing actuator and if still not working will attach the new one. Will update you all next week! Mike
[automerge]1575631464[/automerge]
As I tested programmer using an old one I am going to flush system and change the 3 way valve. I can turn spindle in new one by hand. The old one needs pliers. Probably full of hunk. Hopefully flushing a couple of times leaving water on will help. Once that is done will attach the existing actuator and if still not working will attach the new one. Will update you all next week! Mike
Gunk not hunk!
 
Brown44elz

You need to create a new thread and ask your question/questions there. Jumping in on an already generated post will not get many views or help. You should also be a bit more descriptive with your post as there are many different sorts of heaters.
 
All fixed. Fitted a new 3 way valve and the connected existing mid way actuator...same issue of CH only not working and stat showing dim orange light when not calling for heat. Changed the actuator that came as a set with the TWV and now works fine. All done in a hour or so with a bacon sandwich half way through while system filling up again. Thanks for everyone’s help. Mike
 
Glad you got it fixed Mike. For future reference just so you know from what you described it sounds as one of the internal switches wasnt activating, the motor was motoring over but the switch was faulty not supplying a live from white wire to boiler feed.
Again well done
 
All fixed. Fitted a new 3 way valve and the connected existing mid way actuator...same issue of CH only not working and stat showing dim orange light when not calling for heat. Changed the actuator that came as a set with the TWV and now works fine. All done in a hour or so with a bacon sandwich half way through while system filling up again. Thanks for everyone’s help. Mike
Good to hear your technique of changing parts until you found the right one paid off.
 

Reply to Need help on central heating problem in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Can central heating / gas engineer expert help me with below issue. During winter time only, I have been having issue with low pressure or pressure dropping with unvented hot water cylinder system. During summer time there is no usage of central heating so the pressure at unvented system is not...
Replies
0
Views
566
Heating and hot water is not working. Plenty of heating oil. I have replaced batteries in thermostat and it seems to be working ok, showing flame to call for heat, and the receiver seems to be working ok with green light, but heating is just not firing. I really am not sure what the problem is...
Replies
5
Views
311
Hi All, Hope somebody can help :) I have a vented HW system with a pressurised Ch system but got bit of a annoying issue, when the hot water comes on all seems ok then after about 15/20 mins i started to hear a trickling noise from hw cylinder which i can also hear in the boiler. The central...
Replies
3
Views
455
H
Wishing everyone on tgmhis forum a very happy Christmas!! I am working on a combi boiler which has problem with heating only. Water is heating normally. Here are the symptoms 1. Signal from thermostat is not firing the boiler. It does not make any sound when heating is on from thermostat. 2...
Replies
2
Views
318
I have a home with an oil boiler in a garage turned into a flat, heating both flat and main house, running c plan with two pumps, two motorised valves simple bi-metal thermostat on wall in flat with 4 standard TRV's rarely used so not worried about the flat, and main house has Nest Gen 3 in the...
Replies
0
Views
351
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock