Hi all,

Looking for some advice please.

I have just recently moved into a cottage with an old back boiler system and an Esse muti fuel stove, and I seem to be getting nothing but problems with it.

The main thing is getting the radiators to come on and stay on. Most of the time I can have a blazing fire on and the radiators will come on for 5 mins or so then go back off again. They will then take another 45 minutes or so before coming back on, staying on again for 5 mins, then going off again. This is without putting more coal on the fire. It takes longer between coming on if it is cold outside, or if I have been away for a day.

The other thing is, most of the radiators will only get hot at the top and not at the bottom. They aren't exactly cold at the bottom, just slightly warm. I have bled all the rads and there was no air.

The hot water from the taps is always very hot, even if the fire has been off for a day or two.

Cheers
 
The pump might be operated through a pipe stat. It certainly should be.
That might explain why it is turning on and off. A pipe stat would have to be set precisely to avoid the water boiling before pump turns on. Also don’t want pump running when fire not heating much.
Or your pump is faulty, but unlikely
 
The pump might be operated through a pipe stat. It certainly should be.
That might explain why it is turning on and off. A pipe stat would have to be set precisely to avoid the water boiling before pump turns on. Also don’t want pump running when fire not heating much.
Or your pump is faulty, but unlikely


Thanks.

There is a stat. I can only see one.

On a box behind it, someone has written 45 on it. It looks like a plug socket, without the socket.

Should there be 2. 1 flow, 1 return?
 
I should add that if a pipe stat exists it should be on return pipe just leaving hot water cylinder.
If fitted in wrong place it could cause pump to be switched on too soon or too late and also cause short or long on/off periods.
 
Thanks.

There is a stat. I can only see one.

On a box behind it, someone has written 45 on it. It looks like a plug socket, without the socket.

Should there be 2. 1 flow, 1 return?

Should be just one stat.
The “45” maybe is the setting temperature for the stat that someone has decided is correct for that stat on your system
 

Reply to Multifuel stove with back boiler problems in the USA area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
250
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
2
Views
147
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
5
Views
127
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock