Messages
10
Hi all,

Megaflo 300i in the loft. I noticed the overflow was dripping and also the tundish. 10 second google and lots of instructions how an average user (I'm very average) can recharge the air gap. Followed to the letter:
Closed mains feed to megaflo
Opened lowest hot tap. It drained pretty quickly.
Opened TRV (actually called T&P release valve)

At that point nothing happens - no water flow through tundish, and no gurgling.

Put all back on and it's not dripping but as I didn't really do anything, it can't be fixed can it?

Shall I just leave it till it goes again or is this impending doom?

Thanks for any advice
 
Opened TRV (actually called T&P release valve)
You need to grip it, turn in anticlockwise enough that it opens and starts sucking, and then keep it like that for about 10-20 minutes. If you turn too far (more than about 30° IIRC) it'll clunk shut again.

I suggest you wear a thick working glove on the hand you use to hold the valve open because the spring is pretty strong and otherwise, unless you have plumbers' fingers, you'll be in quite a lot of pain by the time you've finished.
 
Thanks Chuck. It was pretty easy to turn and stayed in the turned position - does that suggest the spring is a bit knackered?

I checked what work was done on the system and in 2019 it had a new TPRV at least that's what the job sheet says, so it should be OK
 
Hi Scott, No it's normal vertical but I did it again following what Chuck said and turns out I was a bit limp when turning the valve. It needed a good hard grip. And now my hand hurts after 15 mins+ of holding it so looks like it worked! thanks.
 

Reply to Megaflo regenerate air gap? in the DIY Plumbing Forum area at PlumbersForums.net

Similar plumbing topics

Morning All I have a Megaflo unvented cylinder . Water had been dripping into the tundish so I tried to recharge the air gap, but when I went to turn the pressure relief valve it would not turn at all, as it usually would. My shower has been dripping in the bathroom next door , could in anyway...
Replies
1
Views
387
Hi. I replaced the Pressure and Temperature relief valve on my MegaFlo CL300 (I had thought it was dripping but it turns out the overflow drip is coming from the 3bar safety relief valve for the red expansion vessel) Before I replaced the valve it would recharge the air bubble normally - the...
Replies
2
Views
447
Good morning! I have a dripping tundish, so decided it's time to replenish the air gap in my Megaflo - something I've done from time to time in the past. So I've turned off the water, opened a hot tap, and then tried to open the pressure relief valve on the Megaflo. But it's stuck: the plastic...
Replies
6
Views
1K
I have a megaflo unvented cylinder on the first floor of my property and I am trying to recharge the air gap. I have turned off the incoming cold mains valve upstream (and right next to) the pressure regulating valve and then opened the hot water taps at the lowest point in the house. The...
Replies
11
Views
4K
Hi issue: No water from hot taps being fed from megaflo. Was having HW pressure issues, obvious from no flow in attic but very low flow on ground floor, so decided to drain and recharge megaflo. After draining megaflo from drain cock (as on ground floor),with lower tap open and odd t&p valve...
Replies
2
Views
5K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock