Hi all, electrician from the dark side looking for your views please.
Background- We are working on an unusual job, bit of a mini castle converted into flats.
Gas has been installed in five flats (not recently) but have never been fitted with main equipotential bonding.
We’ve looked at the properties involved & it’s well nigh impossible for us to run the 10mm bond without major disruption and possible damage to centuries old wall panelling & floors.
In the electrical regs, we don’t have to bond the gas if the copper supply immediately after the meter has an insulating section (plastic?) installed (the pipe can’t then introduce a different potential).
So, question.....is it permissible for a gas safe registered engineer to install such an insulating section?
Thanks in advance for your thoughts.
 
No cant use plastic

But more than likely the supply to the meter will be plastic

Could you use an earth rod (thinking out side of the box) ?
 
Thanks for your thoughts guys. Out of curiosity, is it because gas distribution mains are covered that they can be in plastic, but accessible gas pipe has to be steel/copper?
 
Can’t have plastic above ground

And if it’s been renewed they just install a new plastic pipe through the old steel supply
 
Thanks for your thoughts guys. Out of curiosity, is it because gas distribution mains are covered that they can be in plastic, but accessible gas pipe has to be steel/copper?
UV rays will make it brittle
It’s also easy to cut/damage
 

Interesting question .

Flats raise a number of issues and this isn’t unusual.

The last time I encountered something similar, the incoming gas, all the meters and the incoming lecky and meters and switch fuses were in the same cupboard .... so the bonding cables were all run in the same cupboard

As for an Earth rod, that doesn’t produce the desired outcome of equipotential bonding as the rod would not be connected to the met .....

Hope this helps
 
Folks, apologies for the delay in coming back to this issue. I’m now aware that in the commercial/industrial sector, there is a device which can be installed in/on a copper gas pipe which breaks the (electrical ) continuity of the pipe. Does anyone know if there is a domestic sized equivalent to fit a 22mm dia copper pipe?
 
IGEM/g/5 edition 2, looks like it covers your particular situation.
Appendix 5 covers several different types of multi occupancy buildings.
Also a call to gas safe technical may help find a product that could be used in the UK. you can google the igem doc
 

Reply to Main equipotential bonding to gas supply in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
249
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
5
Views
125
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock