Hi Chaps,

Wife has been nagging me about having shelves in an airing cupboard for about a year now.
We've had unvented cylinder fitted last year and both expansion vessels are very high to fit a towel shelve (as it will be just below the top of door frame).
Can the expansion vessels be lowered so the top of the expansion vessels hit the red line drawn in the picture attached? Are there any minimum requirements for fitting expansion vessels on unvented cylinder?
I would really appreciate advice on this if you're G3 qualified, before I call a plumber in.

Best Regards,
Lumen
 

Attachments

  • Boiler.jpg
    Boiler.jpg
    72.6 KB · Views: 34
Last edited:
Lowering the expansion vessels isn't a problem providing you have space. It looks pretty tight in there and if you do decide to go for it then like you say you'll need a G3 guy as you'll be adjusted both unvented supply and heating pipework
 
As above yes it can be done ? but i would build the sheving around whats there already ,if you move them lower they will still be there just lower removable slated shelving is the way . Kop
 
I think there is not a great deal of clearance below the proposed shelf. have you measured the height of the units and allowing for connection of pipework?
 
Remember on the potable side you must have a continuous fall on the pipework from expansion vessel to connection at cylinder. You must not create a "silt trap". The fall does not need to be big and I suspect that even just level is OK for practical purposes. See link for best practice on this subject.

 

Reply to Lowering Expansion Vessels on Unvented System in the USA area at PlumbersForums.net

Similar plumbing topics

hello we have an unvented system. we have an issue where the hot water is hot for 10 seconds and then luke warm, turn off taps / wait and turn back and it repeats itself. had boiler checked and told it was the expansion vessel. Had the expansion vessel drained and recharged. plumber told me...
Replies
5
Views
666
R
I have Gledhill 300L unvented water cylinder storage system with Vaillant Boiler. We are using it for UFH and radiators. My plumber has fitted 2 expansion vessels 1) Zilmet - 18 Litre Red Heating Expansion Vessel & Sealed System 2) MULTIFUNCTIONAL TANKS WITH REPLACEABLE MEMBRANE Why has he...
Replies
3
Views
2K
rahul sood
R
Hi all. As the title says, I have a problem with an unvented cylinder I had installed last year where the first time I turn a hot tap on after the cylinder has been heated I get what sounds like a vibration. It generally starts about 1s after I open the tap and lasts for about 1.5s. I've...
Replies
27
Views
2K
Hi, We have a large Heatrea Sadia unvented hot water tank, not sure of the size in liters but its about 1600mm tall. The tank is around 3 years old now and was amazing when it was first installed. Around a year ago we had a problem with water dripping from the overflow pipe outside and we ended...
Replies
0
Views
376
B
Context for issue: I'd like to start by saying I'd rather not read 100 "Hire a professional comments", I will do that when/if it comes to it, but I'd like to do it myself if possible. All images for system here: https://*********/a/ngPQkre Last winter the temperature switch on my boiler...
Replies
0
Views
342
Butchy10
B
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock