Dear all, I have a question please kindly help me. The job is in rural area and has very low water pressure. There is no gas here. The customer is thinking to install an electric combo boiler. The problem is the minimum pressure for electric boiler is 1 bar. How can I fill up the combo system? Can I buy Something like a pump to increase the water pressure. I don’t have this kind of experience. Please kindly help.

Thanks guys
 
When incoming pressure is poor ie less than 1-1.5 bar then you should consider mains booster pump and a break tank.
This will have a stored amount water in the tank with an air gap to prevent backflow into mains boosted by the pump to a set pressure.
I'm not a plumber (oil heating engineer) so have not done this type of install but if the incoming pressure is that poor then this is the type of setup you should be looking at.
 
Depends if you just want to fill up the heating once a water pressure testing pump will do that eg rp25

mainsboost any good to you ?
 

Reply to Low Water pressure area in the USA area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
0
Views
49
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
1
Views
46
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
202
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
165
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
175
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock